Hi!

Need some help on a schoolproject!

We have an optical sensor, that counts 12 pulses per rotation on the shaft on a machine.

I would like to convert this information to RPM, it is some kind of function in the PLC i can use, or must I make it myself?

I have tried making a FB but I cant get it to work, it is attached.

Thanks for any help!
 
If you want that PRM value is updated every minute:

Use a timer 1_minute to generate one-shot pulse everuy minute (CLK pulse)

Use a DM0000 and increment it continuosly od each postitive change of IN pulse from sensor.

When CLK pulse is on, then:
-Divide DM0000 with 12
-Stroe reult in DM0002 (that is RMP)
-clear DM0000

Each minute you will get a new DPM data in DM0002.
 
If you want that PRM value is updated continously:

Measure time interval between two IN pulses (from sensor), using internal 0,02sec pulse. (50 pulses counted = 1 sec =1/(60*12) rpm

Reset measurement on falling edge of IN pulse.
 
Last edited:
If you want to use intergated HSC (high speed counter) inputs (if exists on CPU):

Use instructions foh HSC.
 
CJ2 does NOT have High Speed Counters on base PLC! You would need to add either a CJ1W-CT021 HSC module OR a CJ2M-MD21 Pulse I/O module to use HSC functions.
 

Similar Topics

I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
Replies
0
Views
92
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
Replies
6
Views
191
Hi Everyone, i am modifying an OMRON Cj2M program and have run into an issue. How do you find the timer, counter, registers that have already...
Replies
11
Views
709
Hello all, I am trying to set PLC clock using DATE function. When DATE function is enabled, I can see A351 to A354 change to the register...
Replies
3
Views
375
Hi all, i have a hot water tank (500 gallon best guess) that uses a valve controlled by the plc to fill it. there is an analog 4-20 ma sensor...
Replies
26
Views
2,221
Back
Top Bottom