NLP status frequently coming on ATV320 VFD

smartatuls

Member
Join Date
May 2013
Location
India
Posts
30
Hi,

I have a Schneider VFD - ATV320, 1.5kW for a Horizontal motion in which when it is running it shows nLP intermittently in between. First DBR connected was wrong then we replaced with correct one which resolved braking fault problem.

But this nLP is not going at all and it is other VFDs(used for other motions on same machine) as well.

We checked input power by multi-meter and it is ok i.e. 400V - 3Ph during standstill and running condition.
 
NLP means no line power or no line voltage. The drive thinks that there is no input voltage coming into the drive.
Check and verify the line voltage on L1 L2 L3 of the drive. Go to the MON menu and check the ULn Mains voltage to see what the drive thinks the main voltage is.
Verify DC bus voltage on PA+ and PC-. Compare your DC bus voltage readings divide by the square root of 2 to see if it matches the Mains voltage in the MON ULn display.
For example: For 230V rated drive the DC bus should read 324VDC.
 

Similar Topics

Hi everyone i have a customer, who wants to show an alarm on the machine, if the I/O forces are enabled and set, on at ControlLogix L81E with...
Replies
3
Views
145
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
Replies
16
Views
453
Hi guys, I have just recently purchased a 1734-AENTR module so that I could learn how to configure it through LogixDesigner and establish comms...
Replies
1
Views
280
Good morning, I have a system on 1756 L73 that works with supervisor on EN2TR modules. Everything works correctly, except that EN2TR (1) with...
Replies
4
Views
459
Hi. Which of these system bits should I use to know that a particular AI or AO channel is faulted? Like I lost the 4-20mA loop, or the input is...
Replies
10
Views
853
Back
Top Bottom