Regarding a Siemens LOGO! 12/24RCE 6ED1052-1MD00-0BA8 controller...

- What comms protocols does the Ethernet port support?

- Is the port protocol select-able (SIMATIC S7 protocol or Modbus TCP/IP, etc.)?


- Internet search results and the manual are confusing.


Thanks
 
You get them both.

I have used several of these and you can use both the S7 protocol and the Modbus TCP/IP protocol. You can even use both at the same time. (We have only used the S7 protocol to connect with a Siemens HMI)

All the standard I/O External and Internal are premapped both to S7 and Modbus registers. The variables you program can be mapped to a fixed range or S7 tags which also defines what Modbus registers they are mapped to.

I would guess that you could connect to multiple Modbus or S7 devices. It can be connected to like 8 other devices.

Good luck
 

Similar Topics

Hi all, First, thank you for reading the thread. So I had a task as the following: An up-counter must be programmed as part of a batch-counting...
Replies
7
Views
279
Hi Lads, I want to implement a flood prevention system with my domestic water pump. The intention is to have the water pump cut off on a daily...
Replies
7
Views
1,064
We need a Really Simple and Cheap controller that has a display or a Web Interface where we can change some set points. We were thinking about a...
Replies
2
Views
1,030
hello i have LOGO! 12/24RCE and i am looking for a schematics of electronic board. Or if someone know what is the burned component on the photo.
Replies
4
Views
1,395
Hi, I'm no expert in PID regulating so I need some advise. I have a VFD controlled deepwaterpump that is maintaining the pressure in a closed...
Replies
24
Views
11,886
Back
Top Bottom