Raj Kumar

Member
Join Date
Nov 2003
Location
New Delhi
Posts
3
Can any one tell me the commands/application program for getting an voltage output from the Modicon TSX PLC's TSXAMZ 600 analog card. I am not using any analog input and want to get 0 to 10 volt output by providing digital input to control the output of some power supplly. I do not have the literature also to refer. I am using instruction list language and PL7 programming software.
 
Hi

Write a value between 0 and 10000 in the %qwX.4 or %qwX.5. X is the position of the analog card on the TSX Rack.

If you go to Aplication Browser -> Variables -> I/O you can symbolise the output (use a frendly name) and see exactly the output adress.

João
 
What is the actual command ? Is it ST %qwX.4:=xxxxx or S or R %qwX.4:=xxxx

Please write it for me if I want to assign 3000 to the channel 4 of the card installed at position 3 of PLC.....
 
Last edited:
I never used Instruction List. Always use Structurated text or Ladder Logic, but I believe is something like:

LD %M1
[%QW3.4:=3000]

(you must change %M1 according to your needs)

Hope this hepls


João
 

Similar Topics

Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
Replies
18
Views
1,396
hi all, i m using L32e controller and 1769-of4vi analog output card... i m not able to get analog output from it.... can anyone please let me...
Replies
3
Views
1,231
Hello, I have a Micrologix 1400 PLC and using RSLogix 500. Using a Multi Ranger Ultra Sonic Level Sensor and the input is moved to N7:11, then...
Replies
15
Views
3,875
Hello everyone I need logic to see the some analog value getting updated or not. If updated to this ,if not updated do that. Will this work put...
Replies
3
Views
1,668
The application was working in Twincat 4022.16 Used VM for offline. recently changed the laptop and the getting the error with Message as below...
Replies
0
Views
52
Back
Top Bottom