BTR for data and status of 1746 NR8 over Remote IO
jograzn2
Apr 2011
Greensboro, NC
I'm new at working with RIO and have a question I was hoping somebody could please help with.
I've got a SLC 5/05 with a 1747 SN Remote IO Scanner. This scanner is communicating with a 1747 ASB on a remote rack. On the remote rack I've got a 1746 NR8 RTD Input card.
I've sucessfully set up a BTW to configure this NR8 card. I am also getting data back with a BTR.
My issue is that, as I understand it, I can only transfer 8 words through the BTR. Words 0-7 from the NR8 image are the channel data. Is there no way I can ever get 8-15 for the channel status's?
If somebody could point out what I'm missing I would greatly appreciate it.
In the I/O config, change your 1746-NR8 to 1746-NR8 Class 3
The Class 3 option gives you the extra diagnostic data. Then you will need to adjust the block transfer sizes to match.
OkiePC,
Thanks for the reply. I'm sorry I don't see how I can change the I/O config for a remote rack. In my existing file I only see the local racks in the I/O config.
Hello all, I see that the Block Transfer Read instruction can read a max length of 64 words I have a Hilscher gateway to map DeviceNet Slave to...
841
I have been asked to add new hardware to an old system. The PLC is a 5/04 SLC. In local rack, slot 25, is a 1747-SN connected to a 1747-ASB in a...
2,500
Dear Pros, Need help on converting PLC5 to Studio 5000.:bow: I found few BTW/BTR block pointing back to Rack 000, group 0, module 0, which should...
2,214
Hello, I am trying to create a network status map at a plant. I'm assuming the comm status bit of dnet nodes is in the BTR/BTW instruction that...
974
Hello, I have a quick question hoping to get some clarity. I am working with a RSlogix 5 program where a PLC5 processor is communicating via...
2,613