Factory Talk View Studio Comm Set up

Kipper

Member
Join Date
Sep 2014
Location
Belvidere IL
Posts
19
I created a project in FT View Studio. The first thing I did was set up the comm at the end of the tree and added an numeric display programmed it and then verified that it work. I then finish the entire project. In my not so wise ideas I wanted to rename my Device shortcut. Now nothing will talk and its all errors. I changed the name back still no go.
Anyone help me out?
Kipp
 
Before attempting what I suggest below, make a backup of your application using the Application Manager.

When I renamed my device shortcut, with one of my displays open I went to the menu Tools -> Replace... I typed in the name of my old shortcut in "Find what" and the name of my new shortcut in "Replace with".

I had to do this without the Runtime running (I was using FT View SE V10, you might be using ME, I'm not sure). Also, for some reason I had to restart my computer to get rid of a couple of "ghost errors"... not sure why.
 

Similar Topics

Hi all, Attached below is an example of what is happening to our existing SCADA. It seems after patching some Rockwell Software that I thought...
Replies
9
Views
320
The client has an application that when communication between the PLC and the Factory Talk VIEW supervisory fails, the object in the supervisory...
Replies
5
Views
287
Hello all, I am looking for a way to have a user get logged out after an X amount of time because to default so that user privilages are no...
Replies
4
Views
589
Hello everybody. I was wondering if there is a way in FTVIEW Studio to close ) view after x min without interaction . My issue is the following...
Replies
2
Views
364
Is there a way to choose the base font in ME. Text in the Arial Unicode MS which is the default font on my FTVS doesnt show up properly on a...
Replies
1
Views
678
Back
Top Bottom