Old August 9th, 2018, 09:04 AM   #1
Combo
Lifetime Supporting Member
Belgium

Combo is offline
 
Join Date: Jul 2002
Location: Belgium
Posts: 2,672
WinCC connection to S7-300 fail

Hi,

I have a PC with WinCC 7.4 and a PLC 315-2DP with 343-1 card. I cannot get connection to the PLC in the tag management while settings of the ethernet driver seem right...

Any idea what I overlooked ?

Thanks in advance,

IMG_20180809_114641_resized_20180809_020025807.jpg

IMG_20180809_114651_resized_20180809_020023949.jpg

IMG_20180809_114700_resized_20180809_020024970.jpg

IMG_20180809_114704_resized_20180809_020023008.jpg

Kind regards,
Combo
  Reply With Quote
Old August 9th, 2018, 09:53 AM   #2
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,965
I can't see your attachments, not sure why
  Reply With Quote
Old August 20th, 2018, 03:44 AM   #3
Combo
Lifetime Supporting Member
Belgium

Combo is offline
 
Join Date: Jul 2002
Location: Belgium
Posts: 2,672
WinCC

Hi,

Don't know why the attachements were not shown, but I got it online...
I think that placing an IO Field on a screen that requires updating did the connection, is that possible ? So a long you don't ask a tag, the connection could remain in 'not connected' status I think. I'm not sure about this, but that's the impression I got..

Kind regards,
Combo

Quote:
Originally Posted by mk42 View Post
I can't see your attachments, not sure why
  Reply With Quote
Old August 20th, 2018, 11:30 AM   #4
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,965
Quote:
Originally Posted by Combo View Post
Hi,

Don't know why the attachements were not shown, but I got it online...
I think that placing an IO Field on a screen that requires updating did the connection, is that possible ? So a long you don't ask a tag, the connection could remain in 'not connected' status I think. I'm not sure about this, but that's the impression I got..

Kind regards,
Combo
Sounds plausible, at the very least. I know WinCC tries to minimize tag access as possible, managing unused connections seems the next logical step.
  Reply With Quote
Old August 21st, 2018, 05:59 AM   #5
travispedley
Member
United States

travispedley is offline
 
Join Date: May 2012
Location: Sanford, NC
Posts: 91
Not sure about WinCC, but in WinCCFlex/TIA I usually just browse for a tag in the plc and drag it over, this creates the connection for me.
  Reply With Quote
Old August 21st, 2018, 03:49 PM   #6
Thomas_v2
Member
Germany

Thomas_v2 is offline
 
Join Date: Apr 2009
Location: Ger
Posts: 384
Quote:
Originally Posted by Combo View Post
So a long you don't ask a tag, the connection could remain in 'not connected' status I think. I'm not sure about this, but that's the impression I got..
I can say for WinCC 7.3 that WinCC connects to the PLC at runtime start and holds the connection open, even if there is no tag under this connection.
At least it subscribes always to mode transition events like run/stop/warmstart in the PLC.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Confused 1756 ENBT wa5yom LIVE PLC Questions And Answers 24 February 24th, 2015 08:39 AM
communication wincc .Q series and s7 300 ajay34 LIVE PLC Questions And Answers 0 March 30th, 2013 03:54 AM
"Change connection" in WinCC Flexible and Finding the Master Connection lkwythe LIVE PLC Questions And Answers 7 March 11th, 2013 03:26 PM
s7 300 and laptop connection ghanim LIVE PLC Questions And Answers 7 January 14th, 2010 08:29 PM
Siemens CP343-1 U_SEND & U_RECV and S7 connection protocol Esa LIVE PLC Questions And Answers 6 August 14th, 2006 04:19 AM


All times are GMT -5. The time now is 11:32 AM.


.