cpt function and doing the math for silo capacity
remullis
Oct 2012
Georgia
179
I am working with plc5.
I am using the CPT function but getting errors.
The level of the silo is inputed at F51:031. The silo cuft is 3393 with 30' overall height. I need this computed and then I will multiply the Bulk Density to get total tons in the tank.
This is what I have:
(F51:031-0)*(3393-0)/(30-0)+0 ( this is in error)
(Input 17’ in tank -InputMin 0) * (ScaleMax 3393 cuft capacity – ScaleMin 0)/(InputMax 30’ tall tank-InputMin 0) + ScaleMin 0
(17’-0)*(3393-0)/(30-0)+0 = 1922.7 cuft of material in silo at 17’ in a 30’ tank where the cuft of the tank volume is 3393.
Any help would be appreciated.
rm
First question is the bottom of the silo flat or is there a cone ?
The formula for volume of a cylinder is
V=Pi R2 x Height
use that to calculate the volume from the flat bottom up
then if you have a cone calculate the volume in the cone by the level
V=Pi R2 x (Height / 3)
add the 2 together
The | for divide solved my error for the equation. I am able to scale the silo's that are linear (flat bottom). I have figured the silo capacity for a non linear with a cone but of course with the current method above that I am using, when I get to the lower range of the silo I am off some tons.
I have lot's of tanks with varying sizes. Is there a way to scale nonlinear possibly just for the cone volume. I can do the logic to control how I read once it gets down to the cone hopefully. I am trying to avoid programming multiple level points in the PLC5.
I want to average a phorsphorus reading (F8:20) over an hour (4 samples/hr). Ranged 0.03 to 3.0 mg/l. I may want to increase it to 4 or an 8 hr...
5,601
I am using the following formula and I am getting error, Invalid Expression - too many closing parenthesis. when i copy the formula to notepad or...
151
In the CPT in rung 2, i'm having an issue where if there is any value less than 0.0115 in "verticalSpeed", "festoonPosition"'s value does not...
1,113
I have ran into something I have not seen before and wondering if any one had any ideas. The logic I'm currently troubleshooting is using a...
1,657
so I have to find the standard deviation for amperage readings at my plant. when I input the formula into the CPT instruction it is automatically...
1,845