I am doing a system where I have to control a heater on a mold. I will use a PID lood with a PWM output to a SSR to control the heater.
The heater is 1000 Watt, 240V 1 PH.
What I am not sure about is best practice for preventing a runaway condition. I know that when SSR's fail they typically short, allowing current to pass to the heater regardless of the state on the input to the SSR.
I have a bolt on thermocouple on the mold for temperature feedback for the PID.
Is it acceptable to have a contactor upstream of the SSR to open the line voltage if a XXX value above the normal operating range is detected? Im also assuming that this contactor would be in the estop circuit as well, to de energize the heaters in an estop condition.
Can the SAME thermocouple that is used for the PID loop be used to monitor the runaway condition? Or, does a separate thermocouple need to be in place for runaway monitoring?
Im sure there is a standard for this for the US but I cant seem to find it.
The heater is 1000 Watt, 240V 1 PH.
What I am not sure about is best practice for preventing a runaway condition. I know that when SSR's fail they typically short, allowing current to pass to the heater regardless of the state on the input to the SSR.
I have a bolt on thermocouple on the mold for temperature feedback for the PID.
Is it acceptable to have a contactor upstream of the SSR to open the line voltage if a XXX value above the normal operating range is detected? Im also assuming that this contactor would be in the estop circuit as well, to de energize the heaters in an estop condition.
Can the SAME thermocouple that is used for the PID loop be used to monitor the runaway condition? Or, does a separate thermocouple need to be in place for runaway monitoring?
Im sure there is a standard for this for the US but I cant seem to find it.