Member
|
Does Siemens have a product like FactoryTalk View SE?
I am new to Siemens, and just looking into their HMI software.
Does Siemens have a product similar to FactoryTalk View SE? I am looking to have at least 10 HMI clients and two fully redundant HMI servers. I have also developed some standalone projects with Indusoft (Aveva Edge) and just wondering if anyone has experience with a larger plant wide installation with Indusoft? how scaleable is it? Thank you |
![]() |
![]() |
#2 |
Member
|
Take a look at Ignition :
https://inductiveautomation.com/scada-software/ It is customizable, and web based.
__________________
My two cents. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 607
|
They at least used to have a standalone version of WinCC that would run on a PC instead of an HMI. You would use "WinCC Flexible" to program HMIs. I suspect that they continued that distinction in Portal, but it's been a while since I had access to Portal.
|
![]() |
![]() |
#4 |
Lifetime Supporting Member
|
Siemens PCS7 supports multiple redundant servers, and multiple OS clients. I have worked on systems with three server pairs, and over 25 clients.
I am sure the Step7/TIA portal side of things also supports this as well. Contact your local Siemens office for more detailed information.
__________________
Certified Siemens Functional Safety Professional, ID: SFSP17010238 NRA Benefactor |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Nov 2016
Location: Fields of corn
Posts: 2,451
|
WinCC is the product you're looking for. Ken Moore mentions PCS7 which is a DCS implementation and uses WinCC as the SCADA bit.
|
![]() |
![]() |
#6 |
Member
|
I have just downloaded Ignition, and I am going to check out the trial.
I also have WinCC but it looks like you have to run WinCC on Siemens HMI hardware, not deployed on Windows computers?? |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 607
|
WinCC is deployed on PCs. WinCC Flexible is for HMIs.
|
![]() |
![]() |
#8 |
Lifetime Supporting Member
|
You can deploy WinCC on standard PC's. However, when you need tech support, Siemens will often blame the non-Siemens hardware.
__________________
Certified Siemens Functional Safety Professional, ID: SFSP17010238 NRA Benefactor |
![]() |
![]() |
#9 |
Member
|
Sounds like Rockwell...
|
![]() |
![]() |
#10 |
Member
|
So WinCC can do redundant servers? that is interesting...
I will have to do some digging, coming from a Rockwell background, it seems like it is hard to find information on the Siemens website. ( I suppose it's hard to find information on the Rockwell website if you are coming from a Siemens background as well) |
![]() |
![]() |
#11 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2013
Location: MI
Posts: 2,946
|
WinCC is basically the brand name for HMIs from Siemens. It comes in several flavors depending on what you're looking for. What you want is WinCC V7/V8, which is a SCADA class system installed on whatever PC and includes support for redundant servers.
WinCC Flexible is a legacy panel/single station PC system. WinCC Comfort/Advanced inside TIA portal is a newer version of that (but still 10+ years old and near the end of it's lifecycle). WinCC Unified is their new platform that covers the simple embedded panel all the way up to client/server SCADA setups, but it doesn't support redundancy (yet?). |
![]() |
![]() |
#12 |
Member
|
WinCC Professional is what I would compare to be the closest to a SCADA system.
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC. ![]() |
![]() |
![]() |
#13 |
Member
|
Thanks so much for the info... that's exactly what I was looking for
I couldn't figure that out on the Siemens website... too much information |
![]() |
![]() |
#14 |
Member
|
Yeah makes sense, this page should be enough if you want a Siemens option:
https://new.siemens.com/global/en/pr...sional-rt.html
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC. ![]() |
![]() |
![]() |
#15 | |
Member
![]() ![]() Join Date: Apr 2009
Location: Ger
Posts: 511
|
Quote:
Also not all combinations from WinCC Scada are supported in WinCC Prof., like Multiclients which connect to multiple redundant server pairs, separate archive servers and so on. |
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
For FactoryTalk View SE Station single workstation vs distributed | AutomatisationBSL | LIVE PLC Questions And Answers | 4 | April 6th, 2022 04:07 AM |
FactoryTalk View Studio SE clarification | 40mpg | LIVE PLC Questions And Answers | 1 | March 23rd, 2022 04:31 PM |
FT View SE Editing Without License | Mark Cole | LIVE PLC Questions And Answers | 9 | November 22nd, 2014 09:03 AM |
Running FactoryTalk View SE V5.0 to work with FactoryTalk Service Platform 2.40 ? | alpine | LIVE PLC Questions And Answers | 15 | December 15th, 2011 07:49 PM |
FactoryTalk View Studio 6.1 SE Network Project, Display Component not Found Issue | tatsumasa | LIVE PLC Questions And Answers | 3 | September 2nd, 2011 06:54 PM |