Control Logix/studio5000, is there a way to write a force instruction?
In studio 5000, is there a way to write a force mask into a rung?
Long story short, I would like to create a test routine for a FAT test. In this, I would like to be able to individually set certain inputs high for certain conditions. As well as prove that all DI, DO, AI etc are functioning. This is to assist in the fact that what is being built here is only half the story and more inputs from devices that dont exist here are needed to satisfy this. Aside from building an entirely separate PLC setup with ins/outs or other type of microcontroller, I want to find an easy way to make this work. I know there is not a force instruction, but I want something that works likes that. Where I can just point to the device(s), give a mask, and it does the rest. Thanks Folks |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
If you map your inputs to individual bits, and place them in there own routine. You can stop scanning that routine and then toggle the bit states as needed. This was standard at one of my former employers, mad FAT testing, much easier.
__________________
Certified Siemens Functional Safety Professional, ID: SFSP17010238 NRA Benefactor |
![]() |
![]() |
#3 |
Lifetime Supporting Member
![]() ![]() Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,808
|
As Ken stated, it is common to map h/w to internal tags. I see aliasing rarely if at all.
__________________
I don't always test my code but when I do, I do it in production. |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: May 2023
Location: CA
Posts: 3
|
Forgot to mention, this is with SIL2 components using the sil2 AOI for IF16 and IB32.
Because of this, the inputs are mapped to the SIL2 and decisions are made there that would stop me from writing to the bits that have been individualized. Basically, I have to force at the module. I have yet to try skirting around the SIL2... as this is kind of crucial to the whole shebang. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: May 2023
Location: CA
Posts: 3
|
to add more information... 2 IB32s are one in the eyes of the logic. Both must agree or it faults on the channel that didn't agree and it faults the module pair.
1. sil2 pair of modules for inputs with 1492-taifm/tifm interface boards 2. redundant control chassis with RM2, controllers, en2trs. That should help spell out a little more information as to why I am doing things this way. |
![]() |
![]() |
#6 | |
Lifetime Supporting Member
![]() ![]() Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,808
|
Quote:
__________________
I don't always test my code but when I do, I do it in production. |
|
![]() |
![]() |
#7 |
Lifetime Supporting Member
|
What I do for testing is branch to a XIC Test_Bit.
Toggle that bit on or off to test. Sometimes instead of calling them test bit I call them Force or Enable and leave them in after testing
__________________
ivanovaautomation.com Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors |
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Mar 2012
Location: Ontario
Posts: 133
|
Not sure what your AOI does and if logic in the rest of the program references stuff done in the AOI or back to the hardware tags... you can map the required forceable bits in the rungs after the AOI and the rest of the program will use the forced logic instead of the AOI mapped logic.
If the logic inside the AOI is the problem, then perhaps look at COP the field IO into an internal tag with the same data structure and hopefully this can be recognized into the AOI, with force rungs located before the AOI If all of the program logic directly references the hardware tags then you're out to lunch as these asynchronously update on modern processors in the middle of logic scans and cannot be confirmed to be in forced state for the whole program scan. Be cautious when troubleshooting whatever path comes out of this forcing bits, as trending logic most times won't catch multiple state changes within a single scan giving problems with grey areas for actual cause. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
VBA To write tag values in Control logix | nchahal7 | LIVE PLC Questions And Answers | 11 | April 27th, 2017 12:19 PM |
Control Logix DCS instruction "cold start type" | taylor1982 | LIVE PLC Questions And Answers | 3 | November 1st, 2015 11:06 PM |
Motion control: MAG to MAM instruction | memberpeace | LIVE PLC Questions And Answers | 11 | February 26th, 2015 01:37 PM |
Problem: cannot write control word to VLT5000(danfoss), using S7400/IM467 | Sandor-CRX | LIVE PLC Questions And Answers | 9 | May 6th, 2010 12:25 PM |
how often should I trigger the PID? | Ron Beaufort | LIVE PLC Questions And Answers | 11 | February 22nd, 2003 11:57 AM |