M12 Ethernet in Class 1 Div. 2 / ATEX Zone 2
Hi -
I am searching for an M12 panel receptacles to use for ethernet connections. I see lots of M12 cables that are ATEX / C1D2 rated but nothing in the way of M12 receptables (I do see plenty of RJ45). I have concerns with RJ45 durability in a harsh environment (such as RJ45 connectors snapping). I've pretty much used M12 exclusively in cleanroom environments but not in hazardous areas. Does anyone have experience with M12 in hazardous areas? Alternatively, does anyone have positive experience with "ruggedized" RJ45? |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Oct 2007
Location: Nashville, Tennessee area
Posts: 3,493
|
i looked at the Balluff brand we use and they do not list it for hazardous locations. the biggest hurdle i see is that the cable is rated for 4 amps.
what are you communicating with via the cable? i am familiar with the rules in your situation. i was in the munitions industry for 8 years. there are a lot of unknowns right now. james |
![]() |
![]() |
#3 |
Lifetime Supporting Member + Moderator
|
Is the terminals in a C1D2 area or does the cable break the boundaries? Without a lot of details its impossible to help you out.
What Ethernet are you talking about? EthernetI/P , Profi, Ethercat, etc etc. I wouldn't be concerned at all about the RJ45 unless you plan on abusing them. You can see RJ45 on the side of so many industrial robots and devices. If you are putting it in harms way, you need to design the failure mode out of the installation. We have build several protective shield because the customer was concerned.
__________________
There should be a minimum IQ before people can breed. FS Eng (TÜV Rheinland, #11004/15, Machinery) |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
New PC, Dual Ethernet Port Access to Rslinx | SNK | LIVE PLC Questions And Answers | 2 | February 4th, 2009 08:24 PM |
Class I Div 2 panel | sapoleon | LIVE PLC Questions And Answers | 4 | January 18th, 2007 09:39 AM |
Which network should I use? | kra101 | LIVE PLC Questions And Answers | 14 | November 15th, 2006 12:28 AM |
Using a RADES9300 and serial ethernet to connect to plc...Works over eth but not dial | bdoub1eu | LIVE PLC Questions And Answers | 5 | July 28th, 2006 09:30 PM |
RFID for Class 1 Div 2 Hazardous Location | maverick33 | LIVE PLC Questions And Answers | 17 | March 25th, 2006 09:57 AM |