In plant we use Siemens S7 PLC CPU 319F-3 PN/DP with profibus connected to remote I/Os. Profibus network have profibus nodes. We are getting frequent profibus communication failure. Specially during start up of plant after shutdown. We replaced profibus cables/connectors. But still it is happeneing each time.

Could anybody please give some suggestion/advise or document how to proceed to rectify the problem. your reply will be great help.
 
Here's what comes to my mind while drinking coffe on a Sunday morning ;).

1: Check the plug connections; screen properly at the gland plate. All plugs with only 1 cable must have the terminating switch ON.

2: Check the profi network with an analyzer. The ProfiTrace from www.procentec.com is popular.

3: Check the ground connections between cabinets/nodes.

4: The Profi cable is not allowed to be laid close to power cables due to EMC. You can find more about trouble shooting in the handbooks here: www.profibus.com. VFDs and thyristor power units are the worst noise sources.

5: Quick (and dirty?) trick: Change bus profile from "DP" to "User defined". Increase the "Retry limit" to f.x. 5. NB! Click on the calculate button to see if the new times are acceptable for you. Compile and download.

6: You'll find a lot more tips if you search the forum.

Kalle
 
Last edited:
!!Grounding/shielding is very important!!
Everywhere, where grounding is possible, that should be done.
When I have measured lines, most of problems caused by insufficient groundings.
When peeling cable, aluminium foil between wires and metal shield should not be turned over metal shield, because there is insulation layer at the metal foil. Metal shield should have straight contact to connector grounding.
Also cable type is important. Cable has to be profibus cable.

Profibus speed could be also decreased, if there is no "need for speed"..
If speed is "default" 1.5, and threre are lots of connections, stub lines and long cables, speed could be decreased.

All cables should be AT LEAST one meter long, specially if speed is 1.5mbps or more.

Hope these helps..
 
I am at my forth plant straightening out their wiring errors. Most of the time the Profibus cable is too close to the power cables. Look in the MCC buckets and wiring risers on the sides of the buckets. Then look at the cable tray. If any cables are within 4 inches of the Profibus cable, move it. Be especially careful around VFD's. They will screw you up quicker than anything. Usually the symptoms are that you have a motor running and you start something else and the motor you are running stops.
 

Similar Topics

Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
Replies
3
Views
676
Is there a version of Siemens software that can be used to view only the installed program logic and diagnostic buffer to determine system and bus...
Replies
5
Views
2,078
Dear Friends; We have a BOBST 1228 flexo printing machine having Siemens S7-300 PLC (6ES7 318-3EL01-0AB0) and Lenze 9300 and 9400 drives. The...
Replies
3
Views
2,295
I set the Date and Time of the S7 300 PLC equal to that of my PG. But after a few days I found that the date and time were not what they should...
Replies
0
Views
1,909
Hi Can any one give me some of sample project file for Siemens S7 300 PLC that I can practice at home. Thanks in Advance
Replies
2
Views
2,782
Back
Top Bottom