How do I do This????
We are into PLC training and intend to show CPU Redundancy on Siemens S7 412 2DP cpu's.
I have following Hardware
(a) Rack UR2H with 18 slots. 6ES 400-2JA00-0AA00 split backplane bus
(b) Two power supply modules, PS 407 4A
(c) Two CPU 412Dp. 6ES7 412-2Xj05-0AB0
(d) ET200L 6ES7 133-1BL0.0XB0 ( 16 DI 16 DQ)
(e) Set of Profibus cables and piggiback connectors.
(f) USB MPI adapter and cables.
Slot 1 Power supply, slot 2 CPU (MPI 2, Prof 2), Next section Slot 1 Powwer supply, slot 2 CPU ( MPI 3, Prof 3)We have installed Simatic Manager ver 5.4 and SWR software.
What is in our mind is as follows. The programm for IO's on ET200L to be downloaded to both CPU's. One should be master and another standby. In event of main CPU going to fault/ prg mode , other CPU should run programm for these IO's.
Suggestions/sample code WELCOME
BMP of hardware is attached.
Representative image only, Not to be confused with exact Hardware