PV 1000 DH+ Communication

ilhem

Member
Join Date
Dec 2004
Location
Constantine
Posts
74
Hi; can i make a communication with Panel view 1000 (DH+ and rs232 Printer port) by using an rs232 to rs458 (DH) converter or rs232 printer port .
 
No you cant.

now for the why:
DH+ is NOT RS485 (that would be DH485)

now perhaps you can provide some detail as to what you are really trying to do.

get WHAT to communicate with the PV?
 
You may be able to upload/download over the printer (serial) port with a 2711-NC13 cable. Connection with a PLC can only be done with the DH+ port. What is the complete part number for your PanelView?
 
mgvol said:
You may be able to upload/download over the printer (serial) port with a 2711-NC13 cable. Connection with a PLC can only be done with the DH+ port. What is the complete part number for your PanelView?

A complete reference part is:
Pv 1000 2711-T10G8L1
 
O.K., according to your Part Number, you can perform upload/download via the RS-232 port with the cable I listed in the earlier post (you will also have to configure a DF1 driver in RSLinx). To do this, the port must not already be configured for printing (it ships defaulted for upload/download usage). For communicating with the controller, you must connect with the DH+ port.
 
mgvol said:
O.K., according to your Part Number, you can perform upload/download via the RS-232 port with the cable I listed in the earlier post (you will also have to configure a DF1 driver in RSLinx). To do this, the port must not already be configured for printing (it ships defaulted for upload/download usage). For communicating with the controller, you must connect with the DH+ port.
Hi; I can't change a printing configuration to downloding configuration in screen system of PV1000 (only printing chose)
 
Last edited:
According to Rockwell, the only PanelViews that won't support upload/download via the printer port are PanelViews with the following part numbers: 2711-xxx2, -xxx3, -xxx5, -xxx9, -xxx17, -xxx18, and -xxx19. Your 2711-T10G8 should support upload/download over the printer port, unless this published info is incorrect. If you are looking at your config screen and it says "printer", see if you can toggle it by touching it. Also, look in your PanelBuilder32 application file under Application Settings>Terminal Setup. If you cannot change it there (if the selections are grayed-out), I would call Rockwell tech support and get them to explain, since their literature indicates that you should be able to do this.
 
mgvol said:
According to Rockwell, the only PanelViews that won't support upload/download via the printer port are PanelViews with the following part numbers: 2711-xxx2, -xxx3, -xxx5, -xxx9, -xxx17, -xxx18, and -xxx19. Your 2711-T10G8 should support upload/download over the printer port, unless this published info is incorrect. If you are looking at your config screen and it says "printer", see if you can toggle it by touching it. Also, look in your PanelBuilder32 application file under Application Settings>Terminal Setup. If you cannot change it there (if the selections are grayed-out), I would call Rockwell tech support and get them to explain, since their literature indicates that you should be able to do this.

Hi; when i touch a printer bouton on screen systeme of PV1000 ;only activate or not a printer port is set.
 
mgvol said:
Yes, if you "disable printing", it should now allow upload/download over that port.

Thank you , it's ok for upload and download with RS232 printer port if i disable printing ;thank's again.
 

Similar Topics

Hi, I'm wondering if anyone knows whether it is possible to communicate between a Micro820 w/ a 2080-SERIALISOL and a PowerMonitor1000 via Modbus...
Replies
2
Views
544
Hi Guy, some times i receive this message in my PV1000: 637 Communication Driver has FAULTED -contact technical support. after there is no...
Replies
11
Views
3,827
Hi all, after much aggravation trying to get my SLC5/04 to talk half duplex to RSlogix so l then would be able to communicate with both RSlogix...
Replies
0
Views
2,233
i am trying to communicate to my pv1000 by the rs232 port using rs linx which is not detecting the pv1000. please to assist me with this problem...
Replies
14
Views
2,815
Hello, I am trying to use micrologix 1400 Ver.A as adapter and a Productivity P1-540 as scanner, only Ethernet/IP is supported by ML1400 Ver.A...
Replies
2
Views
1,847
Back
Top Bottom