Hello friends
I need to automate a machine, I thought Micrologix 1400 and PanelView Component C1000.
This machine has 2 heating tanks, 1 conveyor, some sensors and actuators.
Actually, there are not PLC and HMI, heating tanks are controlled by simple temperature controllers (Durant TC48, 1 relay output, 1 alarm output, No Remote SetPoint)
In the panelview, Operator will choose a recipe, which one would have configured temperature setpoint for every tank and speed for conveyor, between another
conditions.
I thought 2 options:
Option 1:
Replace temperature controller for another with Remote SetPoint (Omron E5CC-RX3A5M-007)
According with the recipe, PLC will send the RSP for each tank and Speed Reference
Cons.
Actual temperature reading will be displayed just in Temperature controller, not in panelview.
http://imageshack.com/a/img716/2723/6kxb.jpg
Option 2:
Eliminate the actual temperature controller, connect the thermocouples to an 1762-IF4 card and control temperatures through PLC.
http://imageshack.com/a/img706/562/lyxz.jpg
which you think is the best?
Do you recommend another PLC or controller?
How difficult is to control temperature with PLC?
Any comment is appreciated.
Thanks in advance.
conditions.