Wonderware Intouch Value Format

DzakwanAfif

Member
Join Date
Mar 2019
Location
Bandung
Posts
15
Hello, I just need some help here...
I integrate my PLC and HMI through the KepserverEX (OPC). When I check at the OPC quick client, I see that the flow through the pipe is 2.6 m3/Hr.

But when I check at the HMI, it just sends me 3 m3/hr (the intouch make my value increment to 3 m3/hr).

Does anyone know how to fix this? So the value in the Intouch HMI is the same as in my OPC Quick Client.

For another information, the tags I declare is already at IO Real type.

Thank you so much:geek:
 
Try right-click on the text and choose substitute strings. Change ## to ##.# or however many decimal places you want to see.
 