Third party VFD iS7 coms with AB 5380

Jimmyflinn23

Member
Join Date
Jan 2016
Location
brisbane
Posts
6
Hi Gents,

I am currently waiting on 750 series VFD. As it was faulty
The client has got a a iS7 Korean VFD to use.

Does anyone know what to do on the PLC side of things to allow mapping of control?

I get I can install a Ethernet generic module and EDS possible but what else do I need in the plc ie a add on profile to start stop etc.

Cheers Jimmy
 
The i7 drive comes from LS (used to be knows as LG). First thing I would do is to contact them and see if they have developed an AOP for their drive to integrate into Rockwell Logix systems. Lots of drive mfrs have done this for you.
 