TIA Portal 13 over VPN won't let me connect to HMI

I have a machine with a S7-300 CPU and a TP1200 HMI panel set up for remote support through an mGuard VPN router.

I can set up the router connection without a problem and when I start TIA Portal it lets me go online to the CPU, but it cannot find the HMI. If I just ping the network adress of the HMI I get a response so there is something there to connect to, but TIA Portal won't let me connect to it.

I have talked to a technician on site with the machine and there are no issues with the HMI otherwise as far as he could tell.

Any ideas on how to approach this problem this would be appreciated.
  Reply With Quote
Old September 16th, 2020, 02:41 AM   #2
matthew1
Member
United States

matthew1 is offline
 
matthew1's Avatar
 
Join Date: Feb 2011
Location: virginia
Posts: 100
Sounds like a port not configured in the firewall. WinCC dosent use port 102 for online connection. The PG operating system assigns the port I think.

To transfer project WinCC uses Ports 2308 and 50523.

You can telnet the IP with the port number and find out if the port is open. telnet will need to be enabled (most likley) under windows feature. After enabeling open CMD and enter - telnet IP.Address.Of.Device port#

Use the PLC connection as a test. port 102

netstat will also list your ports currently listening or connected when executed.

Mguard may block the telnet traffic also.
  Reply With Quote
Old September 16th, 2020, 03:53 AM   #3
KWLB
Member
Sweden

KWLB is offline
 
Join Date: Sep 2020
Location: Skåne
Posts: 2
I could be wrong here but isn't the point of a VPN that it passes traffic through firewalls? As in, if I have a working VPN connection to the router then any firewalls will have been bypassed already,

And in the PLC cabinet there is just a network cable from the PLC to the VPN router. And I have already tried havingthe HMI plugged straight into the router, that did not change anything unfortunately.
  Reply With Quote
Old September 16th, 2020, 04:24 AM   #4
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,525
Not used a Siemens HMI, so this is a wild guess. :-) With the PLCs when you do an 'extended download' there is a drop down box that lets you choose, 'Show all compatible devices', 'Show accessible devices' and 'Show devices with the same address'. I think it is the first two that won't work over a VPN, so you need to choose 'Show devices with the same address'. Is there anything like that for the HMI?
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Old September 16th, 2020, 05:08 AM   #5
chud
Member
South Africa

chud is offline
 
chud's Avatar
 
Join Date: Oct 2007
Location: KALAHARI
Posts: 966
https://support.industry.siemens.com...=0&pageSize=10

Answer on siemens forum
  Reply With Quote
Old September 16th, 2020, 05:10 AM   #6
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 423
What BryanG said. The same applies if you use a wireless connection.
  Reply With Quote
Old September 16th, 2020, 05:23 AM   #7
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is online now
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 14,377
Quote:
Originally Posted by BryanG View Post
Not used a Siemens HMI, so this is a wild guess. :-) With the PLCs when you do an 'extended download' there is a drop down box that lets you choose, 'Show all compatible devices', 'Show accessible devices' and 'Show devices with the same address'. I think it is the first two that won't work over a VPN, so you need to choose 'Show devices with the same address'. Is there anything like that for the HMI?
Yes there is, and I agree that the latter is the best for connectring via VPN.

Also, for the Siemens HMIS I have had differing results when chosing PN/IE or Ethernet as the interface. Mostly Ethernet works best, but try both.

I use an E w 0 n Router which is similar to mguard. These VPN routers are intended for exactly this use, so typically they will already be setup to open the relevant ports. But if everything else fails, do investigate the ports.

Disclaimer: I think that the transfer dialog has changed a bit from V13 to V14 and to V15.
__________________
Jesper
See my profile interests for Q&A
  Reply With Quote
Old September 16th, 2020, 10:07 AM   #8
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,541
Quote:
Originally Posted by BryanG View Post
Not used a Siemens HMI, so this is a wild guess. :-) With the PLCs when you do an 'extended download' there is a drop down box that lets you choose, 'Show all compatible devices', 'Show accessible devices' and 'Show devices with the same address'. I think it is the first two that won't work over a VPN, so you need to choose 'Show devices with the same address'. Is there anything like that for the HMI?

another vote for this, if using the PN/IE driver.



Quote:
Originally Posted by JesperMP View Post
Also, for the Siemens HMIS I have had differing results when chosing PN/IE or Ethernet as the interface. Mostly Ethernet works best, but try both.

Also, MAKE SURE IT MATCHES between the PG and HMI. Ethernet driver probably makes more sense, since the IP is known, but having someone verify what the panel is actually set for is a good idea.
  Reply With Quote
Old September 16th, 2020, 10:19 AM   #9
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is online now
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 14,377
Quote:
Originally Posted by mk42 View Post
Also, MAKE SURE IT [PN/IE or Ethernet] MATCHES between the PG and HMI.
How is this set on the HMI ? Is PN/IE set when Operating mode is set to "IO Device" and otherwise it defaults to Ethernet ? Or .. ?
__________________
Jesper
See my profile interests for Q&A
  Reply With Quote
Old September 16th, 2020, 10:21 AM   #10
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is online now
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,063
Over VPN, you won't be able to go online with the HMI, only download to it.

You can with the PLC though.
  Reply With Quote
Old September 16th, 2020, 02:40 PM   #11
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,541
Quote:
Originally Posted by JesperMP View Post
How is this set on the HMI ? Is PN/IE set when Operating mode is set to "IO Device" and otherwise it defaults to Ethernet ? Or .. ?

You change it in the Transfer settings window of the control panel (see screen shot). PN/IE is at the top of the list, Ethernet is at the bottom. In their infinite wisdom, they are not compatible.

As far as I know, IO Device activates the "Direct Keys" feature, which allows you to use the function keys of the panel as IO to the PLC. I think it maps the LEDs to outputs as well. The feature was useful on the key panels, I'm not sure how the feature maps to touch.
Attached Images
File Type: png 2020-09-16 14_15_11-.png (48.1 KB, 16 views)

Last edited by mk42; September 16th, 2020 at 02:40 PM. Reason: spelling
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens TIA Portal WinCC HMI Button Removal bagged2drag LIVE PLC Questions And Answers 9 April 15th, 2016 02:40 AM
Display a Data Log on HMI Screen - Siemens TIA Portal LB90 LIVE PLC Questions And Answers 6 April 11th, 2016 10:12 AM
TIA Portal V13 SP1 Comfort HMI Pop-up windows Manglemender LIVE PLC Questions And Answers 4 March 27th, 2016 12:23 PM
TIA Portal HMI Recipe Data Record Uploads DamianInRochester LIVE PLC Questions And Answers 0 December 29th, 2013 02:40 PM
TIA Portal HMI Text Carriage Return DamianInRochester LIVE PLC Questions And Answers 6 December 3rd, 2013 06:40 AM


All times are GMT -4. The time now is 05:45 AM.


.