Unread October 9th, 2019, 02:44 PM   #1
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 108
Compact Logix Problem

Hello Smart People,

I need to take 32 bits in a DINT, and transpose each bit to 32 DINTs.

If bit 00 = 1, then word 00 = 1
If bit 00 = 0, then word 00 = 0

If bit 01 = 1, then word 01 = 1
If bit 01 = 0, then word 01 = 0

.
.
.

and so on...

I want to avoid

XIC mov 1
XIO mov 0

I though about indirect pointer and loop or 1 pre scan, but wondering if there is a better path?

Thanks,
  Reply With Quote
Unread October 9th, 2019, 03:00 PM   #2
Helliana
Member
United States

Helliana is offline
 
Join Date: Nov 2011
Location: Louisiana
Posts: 643
if you want to get fancy and the DINT's can be an array, you could make a loop with indirect addressing. Wouldn't be hard to do in ladder, but would look nice and neat in structured text. You are basically just doing XIC DINT.[INDEX] OTE ARRAY[INDEX].0

Last edited by Helliana; October 9th, 2019 at 03:02 PM.
  Reply With Quote
Unread October 9th, 2019, 03:07 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,893
There's nothing inappropriate about brute force for a simple function like this. It's a very good opportunity to make use of the Add-On Instruction feature of ControlLogix.

Code:
If Source_DINT.0  Then Destination_DINT_Array[0] := 1 ; else Destination_DINT_Array[0] := 0 ; End_If ;
If Source_DINT.1  Then Destination_DINT_Array[1] := 1 ; else Destination_DINT_Array[1] := 0 ; End_If ;
If Source_DINT.2  Then Destination_DINT_Array[2] := 1 ; else Destination_DINT_Array[2] := 0 ; End_If ;
If Source_DINT.3  Then Destination_DINT_Array[3] := 1 ; else Destination_DINT_Array[3] := 0 ; End_If ;
If Source_DINT.4  Then Destination_DINT_Array[4] := 1 ; else Destination_DINT_Array[4] := 0 ; End_If ;
If Source_DINT.5  Then Destination_DINT_Array[5] := 1 ; else Destination_DINT_Array[5] := 0 ; End_If ;
If Source_DINT.6  Then Destination_DINT_Array[6] := 1 ; else Destination_DINT_Array[6] := 0 ; End_If ;
If Source_DINT.7  Then Destination_DINT_Array[7] := 1 ; else Destination_DINT_Array[7] := 0 ; End_If ;
If Source_DINT.8  Then Destination_DINT_Array[8] := 1 ; else Destination_DINT_Array[8] := 0 ; End_If ;
If Source_DINT.9  Then Destination_DINT_Array[9] := 1 ; else Destination_DINT_Array[9] := 0 ; End_If ;
If Source_DINT.10 Then Destination_DINT_Array[10] := 1 ; else Destination_DINT_Array[10] := 0 ; End_If ;
If Source_DINT.11 Then Destination_DINT_Array[11] := 1 ; else Destination_DINT_Array[11] := 0 ; End_If ;
If Source_DINT.12 Then Destination_DINT_Array[12] := 1 ; else Destination_DINT_Array[12] := 0 ; End_If ;
If Source_DINT.13 Then Destination_DINT_Array[13] := 1 ; else Destination_DINT_Array[13] := 0 ; End_If ;
If Source_DINT.14 Then Destination_DINT_Array[14] := 1 ; else Destination_DINT_Array[14] := 0 ; End_If ;
If Source_DINT.15 Then Destination_DINT_Array[15] := 1 ; else Destination_DINT_Array[15] := 0 ; End_If ;
If Source_DINT.16 Then Destination_DINT_Array[16] := 1 ; else Destination_DINT_Array[16] := 0 ; End_If ;
If Source_DINT.17 Then Destination_DINT_Array[17] := 1 ; else Destination_DINT_Array[17] := 0 ; End_If ;
If Source_DINT.18 Then Destination_DINT_Array[18] := 1 ; else Destination_DINT_Array[18] := 0 ; End_If ;
If Source_DINT.19 Then Destination_DINT_Array[19] := 1 ; else Destination_DINT_Array[19] := 0 ; End_If ;
If Source_DINT.20 Then Destination_DINT_Array[20] := 1 ; else Destination_DINT_Array[20] := 0 ; End_If ;
If Source_DINT.21 Then Destination_DINT_Array[21] := 1 ; else Destination_DINT_Array[21] := 0 ; End_If ;
If Source_DINT.22 Then Destination_DINT_Array[22] := 1 ; else Destination_DINT_Array[22] := 0 ; End_If ;
If Source_DINT.23 Then Destination_DINT_Array[23] := 1 ; else Destination_DINT_Array[23] := 0 ; End_If ;
If Source_DINT.24 Then Destination_DINT_Array[24] := 1 ; else Destination_DINT_Array[24] := 0 ; End_If ;
If Source_DINT.25 Then Destination_DINT_Array[25] := 1 ; else Destination_DINT_Array[25] := 0 ; End_If ;
If Source_DINT.26 Then Destination_DINT_Array[26] := 1 ; else Destination_DINT_Array[26] := 0 ; End_If ;
If Source_DINT.27 Then Destination_DINT_Array[27] := 1 ; else Destination_DINT_Array[27] := 0 ; End_If ;
If Source_DINT.28 Then Destination_DINT_Array[28] := 1 ; else Destination_DINT_Array[28] := 0 ; End_If ;
If Source_DINT.29 Then Destination_DINT_Array[29] := 1 ; else Destination_DINT_Array[29] := 0 ; End_If ;
If Source_DINT.30 Then Destination_DINT_Array[30] := 1 ; else Destination_DINT_Array[30] := 0 ; End_If ;
If Source_DINT.31 Then Destination_DINT_Array[31] := 1 ; else Destination_DINT_Array[31] := 0 ; End_If ;
  Reply With Quote
Unread October 9th, 2019, 04:09 PM   #4
BachPhi
Member
United States

BachPhi is offline
 
Join Date: Dec 2007
Location: Los Alamos
Posts: 333
Code:
		FOR i := 0 TO 31 DO
			Dest_DINT_Array[i]:= Source_DINT.[i] ;
		END_FOR;
lol.
  Reply With Quote
Unread October 9th, 2019, 04:18 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,893
Such a simple for/next loop would be ideal, but can't be used in ControlLogix because you can't use the Assignment operator with mixed data types (DINT and BOOL) like this.

The middle line of the for/next loop will fail to compile with a "BOOL tag not expected in expression" error.

The brute force if-then-else method takes more memory, but it compiles and functions correctly.
  Reply With Quote
Unread October 9th, 2019, 04:26 PM   #6
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 108
I could do an indirect rung, would take 32 scans to complete.

I am just doing brute force, at lease it will be easy to understand 3 months from now when someone is looking at it.

Thanks anyway.

I remember doing tasks like this in PLC5, which is why I couldn't figure this out in the logix PLCs
  Reply With Quote
Unread October 9th, 2019, 05:17 PM   #7
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 396
Code:
		FOR i := 0 TO 31 DO
			Dest_DINT_Array[i].0 := Source_DINT.[i] ;
		END_FOR;
lol.
  Reply With Quote
Unread October 9th, 2019, 05:43 PM   #8
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,893
Sometimes dumb is best

Touche'.

But maybe belay the "lol" stuff. It's hard to not come off as snarky or insulting when you employ the text-message language of teenagers. Try "hey, have you considered this method ?".

One drawback of that method is if somebody inadvertently pokes a value greater than 1 into one of the Destination DINT elements; the value will change by 1, but won't automatically go back to 0 or 1 the next time the routine is executed.

The easy way to prevent such a malfunction by setting each sub-element to 0 before executing the assignment line.

Code:
For NDX := 0 to 31 Do;
Destination_DINT_Array[NDX] := 0 ;
Destination_DINT_Array[NDX].0 := Source_DINT.[NDX] ;
End_FOR ;
But when you do, there would be times in between the execution of those two lines during which other routines, interrupts, or communication requests could grab one or more of the DINT[x] elements while they are zero, and before the next line has gotten around to setting the correct value.

Even though those times are very short, it's possible for such an indeterminate condition to cause problems elsewhere in your application.

Last edited by Ken Roach; October 9th, 2019 at 06:06 PM.
  Reply With Quote
Unread October 10th, 2019, 06:53 AM   #9
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 108
I want to thank everyone who chimed in.

This is a great community and home for us!

Paul
  Reply With Quote
Unread October 10th, 2019, 06:54 AM   #10
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 108
BTW, where would be a good place to learn ST?

I have been using Ladder and FB for 25+ years, never ventured down the ST path (yet).
  Reply With Quote
Unread October 10th, 2019, 07:07 AM   #11
kekrahulik
Member
United States

kekrahulik is offline
 
Join Date: Apr 2009
Location: Lancaster,pa
Posts: 321
Several years ago I was looking to do a similar thing where I had set exactly one bit in a DINT to "1" and wanted to have a separate DINT to display which of the 32 bits was on. I asked the forum for advice and Ken Roach was the voice of reason that I needed to hear because sometime you just overthink things.

Yes, brute force - 32 rungs of ladder logic that examined each of the 32 bits. I made that into an Add-On Instruction that I have used in many projects since.

BTW - thanks again Ken!
  Reply With Quote
Unread October 10th, 2019, 10:44 AM   #12
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 346
Which application would you use this trick for? Are you capturing data somewhere and using the 32 DINTS to describe different conditions or something? Like are you capturing data from a barcode off a part, then using the DINTs to determine what part # ?
  Reply With Quote
Unread October 10th, 2019, 10:48 AM   #13
Mispeld
Member
United States

Mispeld is offline
 
Mispeld's Avatar
 
Join Date: Feb 2017
Location: VA
Posts: 445
File Under: Just because you can, doesn't mean you should.

The problem is solvable with a FAL instruction as shown in attached. It took a few attempts.

The first (not shown) attempted to duplicate the structured text approach. However ladder expressions, unlike ST, do not allow BOOL operands.

The second tried to simply bit-shift the source and mask with the value 1. This should have worked, except the presence of the exponentiation operator (**) converts all operands to REALs, even though they are all DINTs, resulting in issues with rounding.

The third used a working array of 32 DINTs to hold the powers of 2, which mostly works except for the overflow error with 2**31. It also fails when the source DINT has bit #31 set, making it a negative number with issues on the shift-by-divide approach.

Finally, the fourth attempt handles all cases that I tested. And by the time it was done, illustrates why a "brute force" set of 32 XIC-OTL rungs (with a FLL clear) is probably the best choice for a ladder solution.
Attached Images
File Type: jpg FAL BITS.jpg (197.4 KB, 42 views)
__________________
"The greatest enemy of knowledge is not ignorance, it is the illusion of knowledge." -Stephen Hawking
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
compact logix l18 and control logix l63 msg instruction Rahul Kumbhar LIVE PLC Questions And Answers 6 February 27th, 2018 10:53 PM
PVPlus 700 communication Problem with Compact logix Sujitdas LIVE PLC Questions And Answers 0 March 17th, 2014 01:18 AM
FTV Studio Compact 1000 Alarm Problem michael90 LIVE PLC Questions And Answers 21 February 20th, 2014 01:28 AM
compact logix versus control logix CPU Nilesh Sinha LIVE PLC Questions And Answers 1 May 13th, 2009 08:30 AM
compact logix prasadgaru LIVE PLC Questions And Answers 0 June 6th, 2008 01:05 AM


All times are GMT -5. The time now is 07:09 PM.


.