Hi,
Trying to get my head around the TIM instruction on a Omron CP1E plc.
The maximum set valve is 9999 which is only 9.9 seconds. (BCD )
What if I want a timer to run for 4 hours ( 14400 sec )

What can I use ?
Can I change the timer base from milliseconds to seconds?

Please tell me there is another timer I can just type the amount of seconds into.

Regards
Andy
 
The TIM instruction is actually a 100mS timer so would range up to 999.9s. Alternately you can use the TIMX instruction which utilizes the Binary range (rather than BCD) up to 6553.5 sec. But that doesn't answer your need for a 4 hour timer.

I've never been real fond of the TIML instruction for long time periods. I prefer to roll my own using the P_1s (CF102) or P_1min (CF104) system bits to increment an integer.
 
Hi Moggie,

I don't seem to have the option of the TIML.
I have the following TIM or TIMX.


I've got a feeling I am going to have to use a 1 second counter.

Andy
 
On a Omron timer in BCD mode, counts are incremented every 100mS.
So that's 10 counts a second. Check out the Omron programming manuals or instruction help file for more details. They explain it very well.
 
The TIML(553) instruction is supported for the CP1E using CX-Programmer v9.6. Not sure why you would be having a problem using it.
 
Not a fan of TIML - restrictions. Use a 1 second or 1 minute pulse into a counter. Easiest way for mine.
 
On a Omron timer in BCD mode, counts are incremented every 100mS.
So that's 10 counts a second. Check out the Omron programming manuals or instruction help file for more details. They explain it very well.

OK, I can see where I've gone wrong. it's actually number of 100msec counts that you enter not actual millisecs.


Thanks for explaining that.


Andy
 
Another approach is to have a scheduled task that runs once every second (or minute) based on the internal clock bits P_1s or P_1min. With a task of this type you can do whatever is needed at a fixed interval.
 

Similar Topics

I have an older CQM1H-CPU21 with cs-programmer 4.0. I have a TIM instruction and I'm trying to lower the time. The value for the timer is stored...
Replies
5
Views
2,181
hello to all I set a timer in omron plc(CPM2A) to count seconds but I have problem here!! time in omron plc is faster than I expect ! I know TIM...
Replies
7
Views
3,146
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
Replies
1
Views
41
Hi dear . I have a system with cj1m cpu11 etn. previously NT 5z HMI was connected with plc. recently my old HMI got damaged. I want to replace it...
Replies
5
Views
75
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
40
Back
Top Bottom