Interested to know the drawbacks of Exd Junction boxes compare to Ex e Junction boxes
chauhanrasikendra said:
does work . I need to know the drawbacks of Ex d JB.
There are absolutely no drawbacks to using an EEx'd' JBox in an application where an EEx'd' JB is required. :ROFLMAO:
However there is a drawback to using an EEx'e' Jbox in an application that requires an EEx'd' Jbox....Its not allowed (n)
EEx'e' means "increased safety", meaning the enclosure:
  • has a high impact resistance,
  • will not hold a static charge,
  • maintains a minimum IP54,
  • contains no arcing or sparking devices,
  • has a controlled internal and external temperature
See IEC regulation 79-7 and CENELEC EN50 019
EEx'd' means "flameproof", meaning the enclosure:
  • will contain an internal explosion
  • has a controlled external temperature
See IEC regulation 79-1 and CENELEC EN50 018
EEx'd' boxes are explosionproof, so they are bigger and more expensive than a normal Jbox. But if you're in a zone 1 location and cannot meet an increased safety standard, you must go with EEx'd'.
also u have a lot of constraints in wiring in EEXe juction box
all componets used must be cetrifed for this use
Hello all, i am planning to start basic plc and programming classes online if anybody is interested mail me
1,398
I keep moving this thing around my garage thinking I will do somehting with it. I did power it up a few weeks ago, and it seems to work fine...
2,194
From time to time I see threads about how to compute the velocity and filter it. The usually complaint is the phase lag that come along with...
36
20,762
I have been looking at this program for awhile now: http://www.cie-wc.edu/Electronic-Engineering-Technology.asp It works for me and my time...
1,855
Hi, I wanted to get into the core of ADC &/or DAC modules. I may have knowledge but it is somehow limited. Oh, well currently I'm doing a...
1,928