jraef
Member
Best advice. The reason for the 1000V Megger on 480V motors driven by VFDs is because when powered by a VFD, there is a potential for voltage spikes to be created that exceed 1000V. If tested at 500V, it's entirely possible for there to be leakage of those spikes that a 500V Megger would not have triggered. Even at 1000V there is a risk of missing some of the worst, but if you are having spikes that exceed the motor insulation rating, you have other problems to solve anyway.I was always taught to use 500v test on 480 DOL motors and 1000V test on VFD (480v) driven motors.
Old darlington transistors, i.e. what was used at the time of the old A-B bulletin 160, were very robust in terms of surviving things like Megger testing. But you can't get those any more, the new ones are smarter, cheaper, faster etc., but are less forgiving.