S7-200 converting to MicroLogix

We have a simple pallet wrapper that we are trying to convert from a S7-200 to a MicroLogix 1400. Out of 119 rungs we're getting stuck on converting two of them (attached).

Everything else appears to be working correctly. Except these two rungs I believe control the number of wraps. Not sure what the Allen-Bradley instructions would equal the Siemens instructions. The MUL is pretty self-explanatory, although not sure about the WAND_W and SHR_W.
Attached Images
File Type: jpg NET61.jpg (24.3 KB, 30 views)
File Type: jpg NET62.jpg (22.3 KB, 24 views)
  Reply With Quote
Old October 21st, 2018, 01:44 PM   #2
nehpets
Member
Wales

nehpets is offline
 
nehpets's Avatar
 
Join Date: Mar 2009
Location: Wales
Posts: 357
The WAND_W is a word 'AND' the two words on the input to instruction are bit for bit AND'ed, and the result is on the output of the instruction.


The SHR_W is a word shift right. the input word is shifted right bit for bit.


Steve
__________________
Why do programmers get confused between Halloween and Christmas - OCT31 = DEC25

Last edited by nehpets; October 21st, 2018 at 01:45 PM. Reason: Spelin
  Reply With Quote
Old October 22nd, 2018, 11:52 AM   #3
chenley
Member
United States

chenley is offline
 
Join Date: Feb 2010
Location: West KY
Posts: 4
Where is the IW0 coming from and the VD8 (Network 61) and VD12 (Network 62) going to? Using the cross-reference IW0 seems to come out of nowhere and VD8 and VD12 only show up on those two lines.

This is my second time in my life looking at a S7 program. All our equipment is A-B based and using cross-reference seems a tad bit different between the two.

Edit: A little more research, I assume IW0 is coming from all the inputs from 0.X? Still can't find much on the VD8/VD12 part except that it is "internal variable memory".

Last edited by chenley; October 22nd, 2018 at 12:03 PM. Reason: additions
  Reply With Quote
Old October 22nd, 2018, 05:02 PM   #4
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,932
Quote:
Originally Posted by chenley View Post
Where is the IW0 coming from and the VD8 (Network 61) and VD12 (Network 62) going to? Using the cross-reference IW0 seems to come out of nowhere and VD8 and VD12 only show up on those two lines.

This is my second time in my life looking at a S7 program. All our equipment is A-B based and using cross-reference seems a tad bit different between the two.

Edit: A little more research, I assume IW0 is coming from all the inputs from 0.X? Still can't find much on the VD8/VD12 part except that it is "internal variable memory".
Fair warning: I haven't used the S7 200's much, they are a bit different from the bigger brothers I'm more familiar with.

Yes, IW0 probably refers to the bits I0.0-I1.7.

I'm not sure about the V memory. It might be tied to some wizards in the project, possibly communications?
  Reply With Quote
Old October 22nd, 2018, 05:27 PM   #5
Jeff23spl
Member
Canada

Jeff23spl is offline
 
Join Date: Jan 2010
Location: Canada
Posts: 807
VB = 8 bits internal memory
VW is a 16bits memo
VD is a 32bits memo

All of them use the same memory map so
(VB0,VB1,VB2,VB3) = (VW0,VW2) = VD0
next adresse in a row after VD0 you get VD4 because a VD use 4 bytes of memory

WAND is a ''AND'' logic of each bit of the word
SHR is a ''shift right'' operation of the number of defined bit at the ''N''

For more info you may look at that manual
http://www1.siemens.cz/ad/current/co...00_2005_en.pdf

Is it blown or you just want it to be AB ?
__________________
Siemens Addict
  Reply With Quote
Old October 22nd, 2018, 07:18 PM   #6
chenley
Member
United States

chenley is offline
 
Join Date: Feb 2010
Location: West KY
Posts: 4
The S7-200 is still good, only having issues with the wrapper arm returning to "home" position, which is determined by a sensor being flagged. 25% of the time, when the wrapper arm is suppose to return "home" it stops 180 out.

Have been troubleshooting it and with our limited knowledge of Siemens logic, figured while troubleshooting it might as well update it to a MicroLogix. Two reasons: 1) The microWin software dosen't seem to like Win7 or Win10. 2) This is the only piece of equipment we have with a Siemens PLC.

Does help greatly knowing that VB0, VW0 and VD0 are all the same, have been looking at it as though they were completely different memory allocations. Looks like I've got more tracing down to do knowing that now. Figuring these two rungs are being used as a sequencer for how the I/O operates.

Thank you greatly for the help thus far.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
S7 300 and S7 200 CPU Communication faisal rasool LIVE PLC Questions And Answers 3 October 25th, 2015 09:37 PM
S7 200 and PPI/PC geniusintraining LIVE PLC Questions And Answers 8 January 5th, 2008 11:02 PM
S7 300 to S7 200 ethernet JOLTRON LIVE PLC Questions And Answers 8 October 24th, 2007 02:11 PM
S7 200 and OPC naishadgosai LIVE PLC Questions And Answers 1 October 8th, 2007 01:36 PM
s7 200 plcs tny LIVE PLC Questions And Answers 2 March 24th, 2006 01:59 AM


All times are GMT -5. The time now is 03:23 PM.


.