I was wondering why are the default engineering units:
High: 16383
Low: 3277

Why wouldn't it be
High: 20000
Low: 4000

And what does adjusting these values actually do?
 
16383 = 16#3fff = 2#0011_1111_1111_1111

If you are running a 14-bit A/D converter, the maximum value is 16383, so 1/5 of that is 3277.

These modules have a 16-bit A/D converter, so I think the default max/min engineering units are meant for compatibility with legacy modules that run in 14-bit mode. 3277/16383 were the min/max for the popular 1746-NI4 analog module in 4-20 mA mode, for example.

I prefer to give up some precision in favor of readability, so 4000 to 20000 is how I set mine up so I can compare the raw values with a multi-meter. I explicitly scale to real "engineering units" like feet/minute or RPM in my controller code.
 
thanks!

Yea I typically put mine to 4000 - 20000 but was just wondering, I do it that way so what I see should match what the unit says it is doing.
Easier to troubleshoot with people. but yes I also instantly scale it to real units Lbs / Temp / ect..
 

Similar Topics

I am running out of real estate in my panel. I have several IE2C cards. I would like to convert them over to IE4C to create space. Rockwell...
Replies
1
Views
1,342
Hi all, This is my first time working with a 1734-IE2C analog module. I am tasked with wiring the flow meter into the analog card and the OEM is...
Replies
2
Views
161
Hello people, I have a 1734-IE2C module which reads a valve position. When the valve is 100% opened the channel data value is something about...
Replies
8
Views
2,273
Hi Guys, We Have some problem with 1734-ie2c module with controllogix cpu, sometimes the input value went to 0 without Module alarm. suggestions...
Replies
1
Views
1,518
We had encounter a problem regarding on our Allen Bradley 1734-IE2C, When we connect 1734-IE2C, to CompactLogix (L18ER), the PLC does not...
Replies
4
Views
4,873
Back
Top Bottom