SLC 5/03 Remote
gbradley
Apr 2002
Corona, Ca.
1,637
On the processor there is a Key switch with
RUN REM PROGRAM
I know you have to have the key switched to Program in order to download a new .rss file, but what is the difference between RUN and REM?
I know REM stands for REMote, and I think that the program will run in either RUN or REM
I looked through the PDF's on This Page
I can't seem to find the answer.
Thank-you
George Bradley
RUN Position
This position places the processor in the Run mode. The processor
scans/executes the ladder program, monitors input devices, energizes
output devices, and acts on enabled I/O forces. You can only change
the processor mode by changing the keyswitch position. You cannot
perform online program editing.
To change the processor mode to Run, toggle the keyswitch from
PROG or REM to RUN. When the keyswitch is left in the RUN
position, you cannot use a programmer/operator interface device to
change the processor mode.
PROG Position
This position places the processor in the Program mode. The
processor does not scan/execute the ladder program, and the
controller outputs are de-energized. You can perform online program
editing. You can only change the processor mode by changing the
keyswitch position.
To change the processor mode to Program, toggle the keyswitch from
REM or RUN to PROG. When the keyswitch is left in the PROG
REM Position
This position places the processor in the Remote mode: either the
REMote Run, REMote Program, or REMote Test mode. You can change
the processor mode by changing the keyswitch position or by
changing the mode from a programmer/operator interface device. You
can perform online program editing in this position.
To change the processor mode to REM, toggle the keyswitch from
RUN or PROG to REM. When the keyswitch is in the REM position, you
can use a programmer/operator interface device to change the
processor mode.
So I can leave the Key in REM and then change the processor from Program to Run with the RSLogix software from my LapTop.
I'll try that Monday Thanks Ron
yeah... i can't think of a single machine in our plant that we don't leave on REM for easy access, except a cardboard baler that we've never had a need to get into.
George. To add to the correct info Ron gave you--be aware that if you are editing a program you can do it with the key in REM, but if the key is in REM and you Download a program the software will cause an electronic shift from REM to PROGRAM, causing the processor to stop running the program. You won't have to physically turn the key. RSLogix will ask you whether you want to do this before it actually does it.
We leave our processors in the REM position as well.
Good afternoon all, I have a SLC 5/04 that I want to add more i/o to, but all out of space on the backplane and no room to increase backplane...
24
5,964
Hi all I have a legacy PLC (1747-L552C) and I have been asked to look at remote access (it's communicating via ethernet to a PVPlus6). I have an e...
1,542
Good Morning , I need to make a online change to a SLC 500 5/05 . Is it safe to turn the key from Run to Remote with causing the processor...
1,866
Hi; At one of our machine, there is SLC5/05 installed. Due to some more I/Os increased at other parts of machine, we want to connect the extended...
2,340
My goal is to get an analog signal from a SLC-500 remote rack back to a PLC-5 main rack. Is this possible? If so, I may need some help. I've set...
1,768