How to check if Load cell is faulty.
bornwild
May 2010
Riyadh
429
I have a load cell to measure the force of the puller. What is the easiest way to tell if load cell is working properly. Also, How do i check if there is a problem with the amplifier.
I would say you need to use a dynamometer or digital force gage to apply force (tension or compression) to the load cell in question and compare readings. I would also suggest that you test the entire range of the load cell to include 20, 40, 60, 80, and 100% of the full range. The load cell can be damaged where it may no longer be linear at certain portions of its range. Not knowing your setup its difficult to say, but if the load cell was not forced beyond its limits, I would start by ensuring that there are no mechanical stresses or forces ( linear bearings binding, load cell axis out of alignment with its load etc) affecting the actual readings you are seeing.
If you have similar laod cell spare, disconnect the load cell electrically and mechanically as well and compare the resistance of all the terminals with new loadcell. In our plant We do confirm this way and most of the time we have succeeded.
Good Luck
Ahh, days of my youth.
you will need some info on the load cell and a multimeter capable of measuring millivolts.
First use the multimeter to confirm excitation voltage to the load cell on the +Exc and -Exc wires at the summation box or at the amplifier.
Colour codes for load cells vary, but common is +Exc(Red) -Exc(Black) +Sig(Green) -Sig(White).
Ensure the +Sense is connected to the +Exc and -Sense connected to the -Exc , if these wires are required.
Note the voltage, example 10Vdc or 12Vdc.
Next, wil no load on the load cell, use the millivolt setting to measure the signal from the load cell on the +Sig, -Sig wires.
Typically load cells have a millivolt/volt rating , usually 2mv/V or 3 mv/V. This means if a 1000lb load cell is applied with 10V volts excitation, at 1000lb of load a full load signal of 20mv , for a 2mv/V rating, or 30mV full load signal for a 3mv/V rating.
With no load , the +Sig -Sig should be close to 1 or 2 mv signal.
Place a known load on the load cell, and the resulting signal should be a percentage of the full load signal based on (Known Weight/Full load weight) * (Excitation voltage * mv/V rating)
You need a weighing indicator, some standard weighs( depend on your load cells capacity, 20% of norminal load is enough to check the load cells is working properly or not. The weighing indicator manual will have detail how to test.
If the load cells is OK, then use a multimeter to check the amplifier is OK or not, test the 4-20mA or 0-10v, 0-5v... output displayed on the multimeter.
I have a 5380 CompactLogix set up with about 50 ethernet devices in the tree, and about 6000 tags being read by an Ignition SCADA instance. The...
2,542
Hello all, I have a Controllogix 1756-L61 with some RIO. There are a couple of 1734-OB4E's that have gone bad. (no output voltage) My boss found...
1,070
Hello I am new here and new to PLC's, I wrote this program for a class that I am taking and my local tech school. The description is switch 7 will...
413
1,971
I'm trying to save a project as an L5X and I need to uncheck the "Encode Source Protected Content" checkbox, but it's grayed out. How do I get...
939