How fast do the tags update in factory talk View SE

sunnyvaleplc

Member
Join Date
Sep 2009
Location
sunnyvale
Posts
12
Hi,

I have a fast analog Input, that changes every 100ms or so, and i want to display that on the Touchpanel (PV1000 -Compact series). I am using the Factory talk View SE edition. How can I change the TAG update rate inside the Facotry talk View SE or the Touchpanel itself to be able to display the 100ms analog value.

Right now, the value is jumping a lot, cause the display is far too slow.

Thanks,

plcguy
 
Right Click the Display and select Display Setting. In the lower left-hand corner you will see were you can select the Max Tag Update Rate.

HTH
 