PanelView Plus ENET very Slow

wa5yom

Member
Join Date
Sep 2003
Location
Ardmore, Oklahoma
Posts
138
I have a PanelView Plus 700 connected via Ethernet to a SLC 5/05.
The application is very simple, pushbuttons, etc.
When I push a button the indicator is vey slow to respond, about 2 to 3 seconds.

Any suggestions?
 
That's a classic beginner's mistake that I've made myself. RSView ME displays (by which I mean one "screen" or "page") are updated all at once, at the rate defined for the display.

The default update rate is 1 second, which makes a lot of first-time projects appear super slow, even when they are connected to a very fast network like EtherNet/IP.

I usually don't set the update faster than 100 milliseconds because that's about as fast as an operator can push a button or interpret information on the screen.
 
Something else to remember is the function key hold time, if it is set high it also will slow down displays on status, IE hold time 0.5 sec,reduce that time will also increase the update rate, just don't set it to 0, defeats the safety factor of that delay time if the key is accidently hit.
 

Similar Topics

Hi Is my first time I post in this forum and also Im new in all this things of PLC programming so I hope someone can help me with this problem...
Replies
6
Views
5,715
We have a Panelview Plus 1000 communicating with a warm backup CompactLogix (L32Es with a 1769-SDN card) pair over DeviceNet. At this stage, the...
Replies
4
Views
2,855
Hi, ive just inherited a project where we have a panelview plus ce screen talking to a contrologix plc over DeviceNet network. Ive worked out how...
Replies
1
Views
1,961
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
78
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
53
Back
Top Bottom