Old February 24th, 2018, 08:40 AM   #1
munguni
Member
Zimbabwe

munguni is offline
 
Join Date: Feb 2012
Location: HARARE
Posts: 13
Valve position control

i bought this motorized ball valve :'' HSH-Flo 1" DN25 2 Way SS304 Motorized Ball Valve,1 Inch Electrical Ball Valve- from china. its model or wiring is CR5-02 FIVE WIRE. OBTAINABLE FROM THIS LINK.,
https://www.youtube.com/watch?v=7DE9tpWQPrs&t=9s

On the basis of this video obtainable from this link, https://www.youtube.com/watch?v=uhINXt8igHU, i went on to buy the valve assuming that it is a 4-20mA as is seen from the second link.

i powered it from a 9volt dc power supply, it works perfectly, but when you try to power it from a PLC, It will not open. i still need to buy 8 more such valves

Does anyone has an idea as to whether the above valve has a position control as suggested in the two videos, and if so what is the wiring diagram required for this control. please note that the diagrams supplied by the suppliers do not have position control requirements

L Munguni
  Reply With Quote
Old February 24th, 2018, 10:22 AM   #2
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,833
1. First link comes up as a video, not a wiring diagram.

2. Why do you see a need to power all nine valves from you PLC? Why not use an external DC power supply?
  Reply With Quote
Old February 24th, 2018, 11:14 AM   #3
damica1
Member
United States

damica1 is offline
 
Join Date: Aug 2015
Location: Illinois
Posts: 595
Use - External Power Supply.
__________________
David M. Camp

Marshall Electric / https://mei-tech.com/monitor-and-control

Please Download from our download section "Monitor and Control" .pdf.
  Reply With Quote
Old February 24th, 2018, 12:47 PM   #4
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 6,253
Is this the unit?

https://www.amazon.com/HSH-Flo-Motor.../dp/B00VPR4U5S

If so it appears to be full open/closed only. The feedback is from the full open and full closed positions.

It appears that this one

https://www.amazon.com/HSH-Flo-Motor.../dp/B0192REJGW

Can be left in a partly open position. But it is positioned by switches not an analog signal. It has no feedback.

And yes, an external power supply for either one.

(Love Google)
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com
  Reply With Quote
Old February 25th, 2018, 10:49 AM   #5
boneless
Lifetime Supporting Member + Moderator
United States

boneless is offline
 
Join Date: Feb 2008
Location: OKC
Posts: 1,473
I would seriously consider my alternatives here, I seriously doubt the quality of this product..
  Reply With Quote
Old February 25th, 2018, 12:20 PM   #6
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,921
I did a lot of control using valves without position feedback. I would simply compare my process signal, such as flow, to the flow setpoint. If it was low I'd use a short contact closure to "bump" the valve open a little. If flow was high I'd bump it closed. If the open or closed limit switch in the valve was tripped I'd know I had hit the limit of control.

An issue with using this valve to control flow is its 9 seconds from open to closed. That sort travel will make control pretty jumpy.
  Reply With Quote
Old February 25th, 2018, 08:50 PM   #7
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 6,253
On reading the data for that second valve I posted

https://www.amazon.com/HSH-Flo-Motor.../dp/B0192REJGW

I see that it's not fully adjustable. It has only two intermediate positions between full open and full closed.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Control valve position feedback russrmartin LIVE PLC Questions And Answers 13 October 17th, 2018 10:37 PM
RSLogix5000 cascade loop PID for valve control mechanizator LIVE PLC Questions And Answers 12 February 1st, 2013 09:37 AM
Injection Molding Control Archie LIVE PLC Questions And Answers 40 October 7th, 2010 03:01 AM
Simple position control made smarter? Brownhat LIVE PLC Questions And Answers 8 June 6th, 2007 10:00 PM
PID for damper position control geniusintraining LIVE PLC Questions And Answers 12 December 21st, 2006 03:05 AM


All times are GMT -5. The time now is 07:03 PM.


.