PLC 5-15 powers up in remote program mode

don1969

Member
Join Date
Jan 2005
Posts
9
I have a 1785-LT B PLC 5/15 processor that on power up starts up in remote program mode instead of remote run mode. The key switch is in remote. I have never seen this before, all our processors are set in remote mode and always start up in remote run mode. Any ideas? Thanks, Don.
 
get online and change the processor status to run,there is a drop down on the top left that at the moment will be in "remote".the key switch can be in either "remote" or "run".
 
If you have an EPROM stuck in the bottom of the processor it may be loading off the EPROM on start. In that case I think it will start in program mode.

Keith
 
Long time since I was in affairs with AB 5/15, but I recall that this is a DIP switch setting in the chassiss it self, if I still remember it is no 8.


Cheers
Hagos
 

Similar Topics

Hello, im quite new and still learning. I would like to ask is it possible for FATEK PLC to read data value more than 16k? I'm trying to move my...
Replies
0
Views
63
Hi all, looking to model old RR relays in PLC. Does anyone have any SPECIFIC examples on how to model a relay such as a polar relay, slow pickup...
Replies
0
Views
95
HelloI need software to download the program from PLC EH-A28DRP from an old machine whose manufacturer does not exist. It may be Ladder Editor for...
Replies
2
Views
108
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
415
Hello, I have a Mitsubishi FX3G 14M PLC and a E615 HMI from Mitsubishi/Beijer. I'm using GXWorks 2 to do the programming and I have no problem...
Replies
4
Views
158
Back
Top Bottom