fault on DP s7-414-3 (leds EXTF y BUS2F)

jmrcalin

Member
Join Date
Sep 2005
Location
barcelona
Posts
27
Hello!
I want to configure a Siemens cpu 414-3 as master profibus and a Controllogix SST-PFB-CLX as slave profibus.
I´ve inserted the file gsd (ssti0876.gse) into the hardware S7 to recognize and configure the slave dp, and it was saved and compiled without fault. But when I´ve downloaded this hardware config to the plc s7 414-3, the plc goes in alarm.
The failures are on CPUside the leds EXTF and BUS2F.
Could someone please help to me?
Regards
 
The LEDs say that there is a problem on the Profibus port. So something has gone wrong with the connection to the SST module.

Is the cable conncetion OK ?
Is the SST module setup correctly with the corract station number for example ?
Also look in the Hardware Diagnostics in STEP7 to get more detailed information about the error.
 
Have I configure the slave profibus (SST-PFB-CLX)before than the Master profibus (S7-414-3) ?. Is necessary configure the module SST-PFB-CLX if it only works as slave?
Regards
 

Similar Topics

Hi Guys, I have a 1769-L24-QBFCB1 that has the OK light flashing on the embedded counter module. The manual states it is a resettable fault, but...
Replies
0
Views
25
The application was working in Twincat 4022.16 Used VM for offline. recently changed the laptop and the getting the error with Message as below...
Replies
0
Views
32
I am working with Twincat 3. I am trying to store some images in files and when PLC restarts I want to read those files and get the images...
Replies
0
Views
38
Hello Everyone. Looking to see if any of you have encountered an issue with these drives. We have a major installation with around 30 of these...
Replies
0
Views
59
Hello, I encountered a problem with the kinetix 6500 drive, error code s22, loss of 3 phase voltage. After disassembling and replacing the thermal...
Replies
2
Views
130
Back
Top Bottom