ControlLogix Modbus TCP/IP Master >4 Devices

I have 6 Modbus devices that I need to get communicating with an L72. Rockwell supplies a program that allows one of their controllers to act as a Modbus master, but it only supports 4 devices out of the box. They do have a rung comment that claims more than 4 devices is possible with modification. Rockwell support (understandably) is not useful for using their program like this, outside their specifications.

So far, I have increased array sizes and added tags appropriately, added rungs, and modified labels. I have gone through the code a dozen times over the past few weeks and just can't hack it. I am pointing all my connections to the same device, connections 0-3 are working fine, 4-5 (the ones I added) are not. Disabling one or more of the working connections does not fix either of connection 4 or 5.

My question is, does anyone have experience with this program and can help? Has anyone successfully modified it to work with more than 4 devices? I am at wits end, I am starting to think it was better to just import RA's supplied program twice and run two instances of it in parallel using local tags instead of global tags where necessary.

Any help would be appreciated enormously, thanks. Let me know if there is anything I can do to help with this process.
  Reply With Quote
Old April 19th, 2019, 02:28 PM   #2
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 1,143
The Spectrum Controls Gateway will do the job and you won't need any ladder logic or messaging of any type in the Logix or the Modbus devices.

https://www.spectrumcontrols.com/pro...ersal-gateway/
__________________
Go Hawks!!!
  Reply With Quote
Old April 19th, 2019, 02:30 PM   #3
JLand
Member
United States

JLand is offline
 
Join Date: Apr 2019
Location: Madison, Wisconsin
Posts: 2
Quote:
Originally Posted by Firejo View Post
The Spectrum Controls Gateway will do the job and you won't need any ladder logic or messaging of any type in the Logix or the Modbus devices.

https://www.spectrumcontrols.com/pro...ersal-gateway/
That looks nice, but only as a backup, as a programmatic solution is more inline with what the budget allows. Thanks, I will keep it in mind.
  Reply With Quote
Old April 19th, 2019, 03:14 PM   #4
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 1,143
True however you might spend more cost in time creating/editing the logic than the cost of the Gateway.
__________________
Go Hawks!!!
  Reply With Quote
Old April 19th, 2019, 05:21 PM   #5
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 2,006
I am familiar with this code and would not recommend you to try to make changes.
There are multiple places in the Master code that have number of connections and transactions hard coded instead of been a parameter through the tag.
You can go rung by rung and see if there is boundary check.
My recommendation is to use Prosoft module.
  Reply With Quote
Old April 19th, 2019, 06:35 PM   #6
harryting
Lifetime Supporting Member
United States

harryting is offline
 
harryting's Avatar
 
Join Date: May 2002
Location: Puget Sound
Posts: 1,984
Quote:
Originally Posted by Firejo View Post
The Spectrum Controls Gateway will do the job and you won't need any ladder logic or messaging of any type in the Logix or the Modbus devices.

https://www.spectrumcontrols.com/pro...ersal-gateway/
Interesting, they are getting in on this game as well. The protocols supported and # of ports supported is still on the short side compared to RedLion's Edge though. Edge can act as OPC UA server and MQTT, for example not to mention the dreaded DNP3 that's common in my world.
  Reply With Quote
Old April 19th, 2019, 06:47 PM   #7
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 1,143
Quote:
Originally Posted by harryting View Post
Interesting, they are getting in on this game as well. The protocols supported and # of ports supported is still on the short side compared to RedLion's Edge though. Edge can act as OPC UA server and MQTT, for example not to mention the dreaded DNP3 that's common in my world.
There is more to come in future firmware releases (which will be field up-gradable). I'm not familiar with the Red Lion product however I can say that Spectrum's Gateway supports all of the listed protocols in one version and you can use them simultaneously (I.E. EtherNet/IP and Modbus/TCP via the same Enet port at the same time) and it doesn't require any software to configure (just a web browser).
__________________
Go Hawks!!!
  Reply With Quote
Old April 22nd, 2019, 12:04 AM   #8
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,368
Seriously, the AB Modbus code is horrendous. It is also HUGE. Using a dedicated gateway probably ends up being much cheaper then upgrading an AB CPU for more memory.


Use a gateway. Spectrum's is awesome, Real Time Automation also makes excellent ones. No hassle, no fuss, no sucking up memory, scan time, no problems with large numbers of end devices...
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Modbus TCP/IP Remote I/O niteman9 LIVE PLC Questions And Answers 12 June 29th, 2015 02:48 AM
Modbus Master not polling the Modbus Slave through an EtherNet/IP Connection mihiri LIVE PLC Questions And Answers 3 July 15th, 2010 02:41 AM
S7 315-2DP / 341 Modbus Master with Multiple Slaves richyr32gtr LIVE PLC Questions And Answers 1 October 13th, 2009 11:05 PM
Modbus Master: S7-200 CPU-224: Port0 halburgepramod LIVE PLC Questions And Answers 0 October 5th, 2009 08:32 AM
is it possible to commutate from Slave to master in MODBUS Protocol baidimed LIVE PLC Questions And Answers 8 November 19th, 2008 08:07 AM


All times are GMT -5. The time now is 04:51 AM.


.