Old February 9th, 2019, 12:05 AM   #16
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: Vancouver, WA, US
Posts: 6,922
NO,NO,NO!!!!!
Ethernet encoders should not be used for any demanding motion control. This application seems to be like a flying shear where one actuator must accelerate to match the speed of a master actuator/encoder. The master encoder should have very fine resolution and be deterministic. Ethernet is not deterministic nor does this encoder seem to have enough encoder counts per revolution. This makes it difficult to computer an accurate master speed. The master speed must be accurate because it is used as the target speed for the slave axis. If the master speed is not accurate then it is impossible to use the derivative gain on the slave axis. It is also impossible to compute a good feed forward for the slave or acceleration feed forward.

Quote:
After a few days I finally figured out that the feed forwards in the axis setup were at 100%
The velocity feed forward should be about 100% on Rockwell motion controllers. I know, remember I wrote the code for the HYD02 and M02AS. The problem is what I described above. The master velocity is for the velocity feed forward for the slave. If the master velocity resolution is as coarse as shown above then the slave velocity feed forward will be just as coarse.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old February 10th, 2019, 11:38 PM   #17
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 385
The resolution on the encoder is terrible. Crank it to 4x quadrature if not using it already.
  Reply With Quote
Old February 11th, 2019, 12:25 AM   #18
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: Vancouver, WA, US
Posts: 6,922
Quote:
Originally Posted by Geoff White View Post
The resolution on the encoder is terrible. Crank it to 4x quadrature if not using it already.
One should always be mindful of how many counts they get per cycle. If there are 100 counts +/- 1 that is not a big problem whereas 2 counts +/- 1 is a 50% change. Even so, how much jitter will be caused by the Ethernet?

I always tell our customers to push our encoder inputs to the limit. We can easily handle 8 million counts or more. That means if the same time is 1 millisecond there are 8000 counts per millisecond on the average. The sampling should result in 8000 counts +/- 1 which is pretty good.

However, all this can be ruined if the master encoder is connected to feed chain driven by a sprocket. Sprockets to not pull a consistent rate so they will also cause sample jitter.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old February 11th, 2019, 02:12 AM   #19
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 385
I believe the OP is using an incremental encoder plugged into an aux port on a drive.
  Reply With Quote
Old February 11th, 2019, 06:59 AM   #20
kekrahulik
Member
United States

kekrahulik is offline
 
Join Date: Apr 2009
Location: Lancaster,pa
Posts: 316
All evidence (and Peter) point to the encoder. Depending on your application, you might be able to fudge it, but a sinusoidal encoder would fix it right.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Logix 5000 motion commands phuz LIVE PLC Questions And Answers 1 March 29th, 2016 11:20 AM
GSV Wall Clock in RS Logix 5000 - Compact Logix L32E alive15 LIVE PLC Questions And Answers 11 February 3rd, 2016 01:17 PM
Logix 5000 install problem smiller LIVE PLC Questions And Answers 16 May 26th, 2015 09:47 PM
Is RS Linx still on and loaded with the RS Logix 5000 CD ? Rob S. LIVE PLC Questions And Answers 5 October 21st, 2014 03:24 PM
rs logix 500 and rs logix 5000 vikas1947 LIVE PLC Questions And Answers 4 March 12th, 2012 06:42 AM


All times are GMT -5. The time now is 02:47 AM.


.