24Vdc Tri-state LED

ranjana

Member
Join Date
Aug 2002
Posts
22
We are building a mimic panel . we have a requirement for Tri-color LEDS.
namely RED-Forward, Green-Reverse , Yellow- faulted.
I want to switch on these leds from PLC. So i would naturally use 24Vdc.

But i could not find LEDS with 24Vdc. All i could find is LED for 2.4Vdc.

Is there any LED manufacturer who has tri color led(Red, green ,yellow)for 24VDC. Also LED size we are looking for is 8mm.

Can you please post their link.

Many thanks
 
Last edited:
Two-colour LED's (red/green) give a yellow or amber light when both the red & green are on.

To make the LED's work on different voltages, use appropriate value current-limiting resistors. Run them on AC with diodes for reverse-bias protection.
 
Yeah, yeah, yeah... so I had a little time on my hands...




PLC Amp Limiting RED
P/S Output-1 Resistor LED P/S
24VDC+ -----\_/----------/\/\/\/\/--------|>|-----24VDC-
Sourcing ohms?? watts?? .7V
40mA

PLC Amp Limiting GRN
P/S Output-2 Resistor LED P/S
24VDC+ -----\_/----------/\/\/\/\/--------|>|-----24VDC-
Sourcing ohms?? watts?? .7V
40mA



. <--- (Dummy Character to keep next line from running off-screen...Phil?)
Assuming Volt Drop across the PLC Output is 0-Volt when the output turns on... what resistor do you need to keep the LED from being destroyed?


Typical LED Characteristics (your milage may vary):
  • Voltage Drop = .7 Volt
  • Amperage = 40 mA
  • Power = approx 28 mW

Voltage Drop across Resistor:
VP/S - VLED = VR

24V - .7V = 23.3V


Resistor Value
VR / IR = RR


23.3V / 40mA = 582 ohms (use the next higher standard resistor value)


Resistor Power Value
VR * IR = PR

23.3V * 40mA = 932mW = 1-Watt

COLOR CONTROL
            RED        GREEN
STATUS Output-1 Output-2 Color
none OFF OFF No-Color
Forward OFF ON GREEN
FAULT ON ON YELLOW (RED + GREEN)
Reverse ON OFF RED

 
Back in the day when Radio Shack was worth a flip, they sold a two lead, tri-state, 5mm LED. Which would be green when forward biased, red when reversed and yellow when an AC current is applied. This is pretty clever as far as the packaging of the LED, but having to deal with a mix of 24V AC and DC would probably be an issue.
 
I have used the 18mm prox type and also the larger 32mm dome. Both are more than bright enough.

I use HMI's on most all machines but sometimes when dealing with a manual operation , a simple light works best.
They are less expensive when you consider the cost of individual lights and labor to wire them.

I have not tried the stack lights yet.
 

Similar Topics

I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
Replies
10
Views
408
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
Replies
1
Views
106
I have begun using 480VAC power supplies in my panels to keep heat from a transformer out of the panel. This works great if the panel is mounted...
Replies
17
Views
4,120
Good morning, could anyone recommend a 24VDC pulse counter which counts up or down to a preset #? Once it reaches this number, send a 24VDC back...
Replies
3
Views
1,643
UL 508: Any reason I can't supply a 60W 24VDC power supply from 2 legs of 480VAC? Our MechE is asking, it is for a product I don't deal with. My...
Replies
12
Views
5,867
Back
Top Bottom