help with a MELSEC FX2n PLC

backstage

Member
Join Date
Jan 2018
Location
austin tx
Posts
1
Our theater’s house curtain controller has a Mitsubishi Melsec FX2n PLC in it that was installed back in ’02. The back up battery failed and of course the program was lost. I have the program on a back up thumb drive as well as a copy of the PLC editing software Medoc. Is this along with an old laptop running Win95 and the SC-09 adaptor cable all I need to reinstall the program? Thanks for any help
 
Theoretically you have all the necessary parts, as long as the cable has the adapter for mini-DIN connector (older cables for FX2C and earlier did not have it).

I recommend that you first execute a clear-all and if the project also has a copy of the data of the D's memory area also transfer it after having transferred the parameters and the program.
 
I would slightly disagree.
Reinstating data (D registers) can have unforseen consequences.
If they are saved in the program (highly unlikely) they would have been saved at a certain point in the automation.
No telling where that would be.

As for your setup.... win 95 needs a batch file to use the com ports.
Medoc is tricky to the uninitiated as it is a dos program.

You have all you need but good luck.
 
About D registers: All the data was lost with battery failure. If there is a copy of those registers in the project, that should be the starting point because it is the only one available. I still recommend that they be transferred ( if the project.dwr file exist)

If they were saved later versions then obviously he should use the more recent set.

I remember that Medoc still worked pretty well in Windows 95, the problems came later with the following versions of Windows.

The latest versions of Medoc, I believe it was v2.3 or 2.4 were also optimized for Windows and I remember having used them on Windows XP without major problems.
Good luck !
 
Last edited:
I mean the battery backed D registers that can contain configuration values.

On the FX2n file registers occupy the same area that D battery backed registers: from D1000 to D7999
 
Last edited:
Melsec Medoc does not save D registers automatically. It is a separate procedure, which creates a .dwr file. If there is no such, there is no data backup. The logic, however, may be not relying on any non-volatile data in the registers.
Also, Medoc has no ability to save the latched M bits status. I there are such in the logic, they will have to be properly set manually.
 

Similar Topics

Hi, I didnt thought i would come across an A1N CPU in my life. But now i have and it is as i thought programmed in MEDOC 2.4.🙃 Is it...
Replies
7
Views
2,969
I have the unfortunate duty to test an AD71 positioning module..the problem I'm having is the test setup in the manual for the drive I'm using...
Replies
1
Views
1,703
Hi, I'm new to the melsec system and I need to install CC links on some processing equipment. I have no ideal how to address the CC link cards or...
Replies
1
Views
3,810
I want to reset a bunch of memories in my program and I was looking for a zonereset function but can't seem to find one. The FMOV function only...
Replies
2
Views
2,258
Hi guys I have installed GX Simulator into its default installation folder/directory. Which i am having trouble finding where the .exe file for...
Replies
3
Views
6,011
Back
Top Bottom