Using UTP Patch cord cable instead of IE cable

Adenitz

Member
Join Date
Feb 2010
Location
tir
Posts
41
Hello guys,

can I use RJ 45 UTP Cat 6 patch cable instead of Industrial Ethernet? The connector is broken and there wille be some deliver time to get identical replacement.
Original cable is this one.

And I have 10m patch cables like this one..

This cable is not shielded, but length is only 10 m and most of the cable is placed inside the control cubicle.
I have tried and it works, but wonder if there might be some restrictions or safety issues I need to watch out.

Thanks!
 
hi i would use a cat6 or 7 cable and make sure it is not routng past VFD cables or solenoid valves etc and then replace ASAP with correct one
 
hi i would use a cat6 or 7 cable and make sure it is not routng past VFD cables or solenoid valves etc and then replace ASAP with correct one

+1

A cat 7 is the same and should cost less, also the Siemens cable is too rigid, you need a pipe bender when installing :)
 
Should be fine for now, but to avoid weird noise issues you do want to replace with a shielded cable at some point.
 

Similar Topics

Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
18
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
1
Views
31
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
Replies
4
Views
59
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
146
I am trying to set up a piece of equipment with a Horner HE-X4R. I'd like to use structured text and so far I'm just trying to get a basic On/off...
Replies
0
Views
59
Back
Top Bottom