Angry PV600 comm problem

I have a PV 600 (2711-T6C16L1, Ser-B Rev-C, FRN- 4.43) It has a RS 232 port I believed is used for printing, and a RS 232 DF1 port.

I am trying to RS Linx with it using an NC 13 cable on the DF1 port. No luck! Help? I would like to wipe any old program out of it and use it wherever it would help.
  Reply With Quote
Old January 19th, 2016, 03:08 PM   #2
timothymajka
Member
United States

timothymajka is offline
 
timothymajka's Avatar
 
Join Date: Oct 2015
Location: FL
Posts: 14
The RS232 port is probably set up for DH484 get your 1747-UIC out and put a serial cable on it, dont forget to move the switch. auto config will not work, set linx up Device: 1770-KF3/1747-KE Baud: 115200 Parity: Even Error Checking: CRC Stop Bits: 1 Protocol: Full Duplex and whatever your computer is seeing the UIC for a comm port
  Reply With Quote
Old January 19th, 2016, 03:13 PM   #3
RickParrot
Member
United States

RickParrot is offline
 
Join Date: Nov 2015
Location: Iowa
Posts: 68
How are technicians/ engineers supposed to know all that. My odds are better winning the Powerball than to stumble on the settings you gifted to me. I will try them. Don't know if I have a 1747-UIC.
  Reply With Quote
Old January 19th, 2016, 03:31 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,011
The part number 2711-T6C16L1 tells us that the communication serial port (not the printer port) is set for DF1 Full Duplex communications. That's the port labled "RS-232 DF1".

It is definitely not DH485. A 1747-UIC will not work with it.

PanelView Standard terminals use a "DCE" type serial port. To connect it to a PC, you need a "straight through" serial cable.

The common 1747-CP3 serial cables for SLC-500 controllers are null-modem type, not straight-through.

The 2711-NC13 cable is a straight-through serial cable, or you can use any off-the shelf cable that has pins 2, 3, and 5 one end connected straight through to pins 2, 3, and 5 on the other end.

The default settings for a DF1 Full Duplex driver in RSLinx Classic should work with the PanelView Standard. Delete your driver and start from scratch with a new driver instance.

Are you using a USB/RS232 converter ? Some of those are lousy and many of them won't work with the Autoconfigure feature, which is why I always recommend simply creating a new driver instance and using the default settings.
  Reply With Quote
Old January 19th, 2016, 03:40 PM   #5
RickParrot
Member
United States

RickParrot is offline
 
Join Date: Nov 2015
Location: Iowa
Posts: 68
Oh, great. ANOTHER cable I have to order. My company has two PICs but no UIC. ARRRRGH!
  Reply With Quote
Old January 19th, 2016, 03:45 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,011
A 1747-UIC will not work with it.
  Reply With Quote
Old January 19th, 2016, 03:46 PM   #7
RickParrot
Member
United States

RickParrot is offline
 
Join Date: Nov 2015
Location: Iowa
Posts: 68
Ken, Thank you for saving me the purchase of the UIC. I am not using a USB/RS232 converter. My programming laptop was ordered with a serial port. I do have the 2711-NC13 equivilent. I made it myself and tested the pin out. Ill wipe the DF1 driver and start again.
  Reply With Quote
Old January 19th, 2016, 03:54 PM   #8
RickParrot
Member
United States

RickParrot is offline
 
Join Date: Nov 2015
Location: Iowa
Posts: 68
Wiped all drivers, closed Linx and reopened. Com1, , SLC/ Micro/ Panelview, Starting baud rate, 19200, station number 00, parity, none, Error Checking, CRC, Stop bits- 1, Full Duplex.... Auto Config and ...... NOTHING! Time to go home!
  Reply With Quote
Old January 19th, 2016, 05:33 PM   #9
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,093
Quote:
Originally Posted by RickParrot View Post
Wiped all drivers, closed Linx and reopened. Com1, , SLC/ Micro/ Panelview, Starting baud rate, 19200, station number 00, parity, none, Error Checking, CRC, Stop bits- 1, Full Duplex.... Auto Config and ...... NOTHING! Time to go home!

Double check your cable (straight thru)

Pin 2 to 2
Pin 3 to 3
Pin 5 to 5

Default settings for your PV is.. See pdf
Attached Files
File Type: pdf defaultsettingDF1.pdf (33.2 KB, 9 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old January 19th, 2016, 09:54 PM   #10
GlenGineer
Member
United States

GlenGineer is offline
 
Join Date: Jan 2014
Location: Manchester, NH
Posts: 122
Just off the top of my head I believe it is the "Printer" connection that you need to connect to in order to program the PV600. You need to get into the settings and change the printer to disabled. After that the panelbuilder 32 software should be able to communicate.
  Reply With Quote
Old January 19th, 2016, 10:13 PM   #11
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,093
Quote:
Originally Posted by GlenGineer View Post
Just off the top of my head I believe it is the "Printer" connection that you need to connect to in order to program the PV600. You need to get into the settings and change the printer to disabled. After that the panelbuilder 32 software should be able to communicate.
FYI, you can use both if the printer is disabled. (either/or)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old January 20th, 2016, 05:04 AM   #12
timothymajka
Member
United States

timothymajka is offline
 
timothymajka's Avatar
 
Join Date: Oct 2015
Location: FL
Posts: 14
Just set up a test app with a PV600. Validated with no errors. Comm protocol DHH485. Just because part number lists it as a 232 port does not mean that the terminal cannot be configured as 485.
  Reply With Quote
Old January 20th, 2016, 10:14 AM   #13
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,093
Quote:
Originally Posted by timothymajka View Post
Just set up a test app with a PV600. Validated with no errors. Comm protocol DHH485. Just because part number lists it as a 232 port does not mean that the terminal cannot be configured as 485.

You can't just configure a DF1 Standard PanelView for DH485, it would take a hardware change and probably firmware.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; January 20th, 2016 at 10:17 AM.
  Reply With Quote
Old January 20th, 2016, 10:19 AM   #14
timothymajka
Member
United States

timothymajka is offline
 
timothymajka's Avatar
 
Join Date: Oct 2015
Location: FL
Posts: 14
I have several machines running 485 out of the 232 port. Not using a blue hose either. The only way to talk to them is 485 with a UIC
  Reply With Quote
Old January 20th, 2016, 12:44 PM   #15
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,093
Quote:
Originally Posted by timothymajka View Post
I have several machines running 485 out of the 232 port. Not using a blue hose either. The only way to talk to them is 485 with a UIC
Thats true, but you cannot just reconfigure a standard PanelView's DF1 RS232 port to DH485 with a software (PanelBuilder32) configuration.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Upgrade PV600 (RS-232-DH485) comm. to ML1500 to PV+ nicer LIVE PLC Questions And Answers 35 July 1st, 2015 05:05 AM
PV600 Comm Issue GoPackGo LIVE PLC Questions And Answers 3 October 7th, 2008 05:51 AM
PV600 1747AIC electrical problem hafas LIVE PLC Questions And Answers 0 February 18th, 2008 06:43 AM
Ancient Panelview Comm problem jrs2563 LIVE PLC Questions And Answers 3 September 4th, 2007 04:01 PM
I/O Comm. problem btw PLC & HMI WFox LIVE PLC Questions And Answers 7 December 31st, 2003 01:09 PM


All times are GMT -5. The time now is 01:43 AM.


.