PV+1000 to PV+6 1000 upgrade
JJGroezinger
Nov 2017
Ohio
Hello,
I've never had to do this conversion yet so I was curious if there are any "gotchas" etc to watch out for.
I know the *.mer should load naively with the pv+6 except that the current pv+ is using RIO which isn't supported with pv+6 so that will be changed to use rs232/DF1. The plc is has a 5/05 with an unused serial port. The current pv+ is connected using an RN6 add-on card to a 1747-SN card on the PLC.
What I've done so far to prepare is to load up a XP VM with FTView 5.0 to recover the *.mer back into a project (I don't have the original project files) and did the tag conversion for 64 bit and was able to load it into FTView 9 on a windows 10 pc.
Is there anything else I need to do before I download it to the replacement panel other than removing the networking config for RIO and then setting up the serial?
One silly thing that got me.....
If you remove a PV+1000, to install the Plus6 of equivalent size, its likely you will need an adaptor plate. Its an extra $200...
Or go with a larger PVP6 and cut a larger hole. Of course they couldn't maintain the original size!
I have a mer or apa file for Pv1000 (2711p-rdt10c) and i need convert this files for Pv5000 (2715P-T15CD-K). Are exist a conversion tool for this...
860
Hi, im looking to migrate a 2711-K10C10 to a 2711P-T12W21 Panelview Plus 7 Standard. I migrate the PV1000 application .pba file in FactoryTalk...
1,971
Hi there everyone! Long time lurker, first time poster. I am doing an SLC-5/03 to CompactLogix migration and am having an issue with a barcode...
1,051
Hi, I'm investigating the feasibility of communication between a old PV standard display and a logix L5X controller via the controller serial...
1,459
Hi all, Anyone manage to get this smorgasbord of hardware to cooperate with each other? PLC - Micrologix 1500 1764-28BXBAA CH1 config - DF1 Full...
1,492