In my project, there are three control valve
One of the hot water line with a diameter of 200
Another on the cold water line with a diameter of 100
And a third on the way mixing cold and hot water with diameter 200 installed. after the third valve
One flow meter is installed
And at the end of a temperature transmitter installed.
Please define:
TIR
FICQR
DN200 (2 instances)
DN100
We will also need to know what control system you are using?
Without detailed information you will not get a detailed answer.
Pretty vague...
If PV is below SP, open hot water valve
If PV is above SP, open cold water valve
I can't see the advantage of the thirs valve or the flow meter
The PLC brand and model is very relevant to the man trying to write the program. Try running a RSLogix program on the TeleTelemecanique to find just how relevant!
I can't see the advantage of the third valve or the flow meter.
The Hot and Cold valves should set the proportion of hot-to-cold (maintain the warm-water temperature in the Mixing Tank to a Temperature setpoint, each with a feedback signal from the Temperature transmitter). The third valve should control the output flow rate to the setpoint rate, and the flowmeter reads the flow rate (feedbck signal to the 3rd flow control valve).
I humbly admit to not reading the original post fully. I'll blame it on my smartphone not resizing correctly, although it probably did...
Just want to put the question out to the PLC guru's... What is the best permissive logic for an Allen Bradley PLC MSG logic? I have seen message...
3,350
Hey all, I'm looking for a little advice. I developed a system with 16 different lines, and a color injection. This mixes all the raw...
2,600
What do you guys use for a small compact installation? The setup is for just 1 input. A pulse off a scale and then send it to another plc.
20
4,771
Hi Guys, Iam just plain curious. How do u proceed debugging a SLC 500 program which has no descriptors in it? Recently i has to do one and it took...
5,422
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
485