How to get scaled 4-20mA temperature sensor signal in PLC
AB2005
Nov 2006
Soth Asia
310
Hi;
I have installed a temperature and humidity sensor Autonics THD-R-C which gives 4-20mA signal out. The signal is connected with Fatek PLC’s analog input card. This is first time I am working with 4-20mA analog signal rather 0-10V for which I need some guideline to get the signals scaled.
According to manual of sensor, at -19.9C it gives 4mA and at 60C it gives 20mA. In PLC, the coding format is 14bit (0 – 16380). Now how do I scale the values to get exact temperature data in PLC?
First please tell us what PLC model and analog input model that you use.
Then you should use this function (FUN 32 ADCNV) in this link below to convert 4-20 mA to raw value and need to set Analog Module to Bipolar Mode (-8192 to 8191)
http://www.esea.cz/support/fatek/Supplement_FBs/FUN32-ADCNV.pdf
Then convert into temperature value by this equation
Temperature Input = (Raw Value from FUN 32) * (60+19.9) / 16383
I'm pretty new to PLC's, so forgive me if I use the wrong terminology and whatnot. We have an issue at work where we have a flow meter that is...
271
Pretty simple question, but I was wondering how I can set the Analog Output 1 of an S7-1200 (DC/DC/Relay) to be proportional to a data tag. I...
834
Hello - you folks were kind in helping me the other day so I'm back for more... My program is finished however the end customer hasn't provided...
1,911
Hi everyone. New to RSLogix5000 and learning as much as I can. I'm much more familiar with Omron. Is it required I select "scaled for...
1,824
Good Afternoon , I have some new machinery that I need to tell another machine what speed I am running. The analog output card that I am...
2,690
