control logix module failure identification
PSpal
Jan 2011
surat
52
we are using both control logix 5555 module with CNB/ENBT/with 1756IB32/OB32 , 1769-HSC MODULE ETC. The problem is that when the processor goes to fault due to any of these card failure , it takes a longggggg time to identify the same as there is no information in "fault description " for which module has failed . BUT IN OLD SLC 500 SYSTEM, the fault description contains the chessis no which is probably faulty. which helps to identfy easily..
IS THERE ANY OTHER PROCEDURE TO KNOW WHICH MODULE IN CONTROL LOGIX CHESSIS HAS FAILED???
There is a good programming manual for the ControlLogix family that includes details on how to use the Get System Variable (GSV) instruction as well as other methods to monitor the connection status and health of ControlLogix modules and network connections.
It's called the "Logix 5000 Controllers Controller Information and Status Programming Manual", Publication 1756-PM015.
http://literature.rockwellautomation.com/idc/groups/literature/documents/pm/1756-pm015_-en-p.pdf
In fact, search the Literature Library using the Publication Number keyword "1756-PM" and I think you'll be impressed at the variety of ControlLogix family programming guides that have been developed over the past ten years or so as additions to the original three Instruction, User, and Motion guides.
I have am trying to determine if I can use a 1756-IB16I (or some dc input equivalent) to handle a 24vdc input pulse frequency of 80 pulses per...
916
Hello All, Can you check the below configuration and tell me how to check the module status of modules in the secondary rack of a redundancy...
495
Hi all, I have an application where there is a Control Logix PLC connecting to a B&R remote I/O station over Modbus TCP via a prosoft MNETC...
1,907
Hello. I am still fairly new to this. I am playing around with an Indradrive HCS01 controller. I have it talking to my L71 (V33.11) just fine...
2,340
After being power cycled rapidly several times by an unhappy power supply 3 out of 6 1756-IB16/A modules are now shown as Unrecognized Device...
1,621