Omron Differentiate

Howdy

Having a poke at some Omron code, and run into a scenario I didn't think should work. A TIMX on the end of a rung with preceding contacts. The thing I dont understand is the contacts are differentiated, so would have expected the timer not to run other than a single scan ? I put the ladder in simulate mode, and seems to work as if not differentiation ?

Haven't seen the ladder running in the PLC, so not certain isn't a simulate issue ? Any info useful..

Cheers Chris
Attached Images
File Type: jpg ladder.jpg (157 Bytes, 114 views)

Last edited by Lemming; April 11th, 2019 at 06:40 PM.
  Reply With Quote
Old April 12th, 2019, 05:58 AM   #2
gtsuport
Member
United States

gtsuport is offline
 
Join Date: Feb 2005
Location: Grand Rapids, MI
Posts: 1,153
Can you re-post the image.
It did not get uploaded.
gtsuport
  Reply With Quote
Old April 14th, 2019, 06:44 PM   #3
Lemming
Member
New Zealand

Lemming is offline
 
Join Date: Oct 2004
Location: PalmerstonNorth
Posts: 331
With pic, hopefully..
Attached Images
File Type: png Ladder1.PNG (24.7 KB, 86 views)
  Reply With Quote
Old April 15th, 2019, 09:57 AM   #4
BITS N BYTES
Lifetime Supporting Member
United States

BITS N BYTES is offline
 
Join Date: Jun 2005
Location: Miami Beach
Posts: 415
Downward Differentiated Instruction
Attached Images
File Type: jpg Downward Differentiate.JPG (47.6 KB, 67 views)
  Reply With Quote
Old April 15th, 2019, 01:50 PM   #5
Lemming
Member
New Zealand

Lemming is offline
 
Join Date: Oct 2004
Location: PalmerstonNorth
Posts: 331
Yep, that's how understood they work. So given the TIMX needs an input on to decrement, cant work ??

Prob safest to wander off to site and plug in to confirm
  Reply With Quote
Old April 15th, 2019, 02:04 PM   #6
sbaum
Member
Canada

sbaum is offline
 
Join Date: Mar 2009
Location: Ontario
Posts: 141
Your rung is always true, so the downward differentiate will reset the timer if any of those conditions transition from 1 to 0.
Better take a closer look at the timing chart Bits N Bytes posted.

Those differentiate are very handy but it can take a bit (no pun intended) to wrap your mind around them.
  Reply With Quote
Old April 15th, 2019, 02:48 PM   #7
Lemming
Member
New Zealand

Lemming is offline
 
Join Date: Oct 2004
Location: PalmerstonNorth
Posts: 331
Yeah, just looked at the instruction help posted by BITS N BYTES again, and can see now thanks.. Not how I expected it to work.. (my preconceived idea got in the way of the help file :-) I thought any diff contact was true for a single scan only, but makes sense that can also be not true for a single scan as well.

Thanks for the replies
  Reply With Quote
Old April 15th, 2019, 03:35 PM   #8
Lemming
Member
New Zealand

Lemming is offline
 
Join Date: Oct 2004
Location: PalmerstonNorth
Posts: 331
Out of interest, where did you find the timing chart ?

I looked at the help file baked in to CX, and it stated the output ON for one scan on either LD or NOT_LD depending on the transition and diff applied. Couldn't find any reference to how it actually works..

So if using a NOT_LD with a diff up, is OFF for 1 scan on the bit rising edge ? I'm assuming the rung in the image resets the timer on any transition of the 4 bits ?
Attached Images
File Type: png ladder3.PNG (19.4 KB, 41 views)
  Reply With Quote
Old April 15th, 2019, 06:58 PM   #9
BITS N BYTES
Lifetime Supporting Member
United States

BITS N BYTES is offline
 
Join Date: Jun 2005
Location: Miami Beach
Posts: 415
http://www.plctalk.net/qanda/showthr...324#post620324
  Reply With Quote
Old April 15th, 2019, 07:33 PM   #10
Lemming
Member
New Zealand

Lemming is offline
 
Join Date: Oct 2004
Location: PalmerstonNorth
Posts: 331
Thanks heaps
  Reply With Quote
Old April 16th, 2019, 07:50 AM   #11
BITS N BYTES
Lifetime Supporting Member
United States

BITS N BYTES is offline
 
Join Date: Jun 2005
Location: Miami Beach
Posts: 415
[quote=Lemming;813191]Out of interest, where did you find the timing chart ?

/quote]


It,s in the programming manual for each PLC. Just search for "differentiate".


  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
trouble with 1769-SDN devicenet scanner - lost Omron NE1A node bboytaktix LIVE PLC Questions And Answers 1 August 2nd, 2017 01:42 PM
Programming Omron PLC, some basic help is needed arbj LIVE PLC Questions And Answers 3 June 14th, 2015 02:00 PM
Omron Security FAIL oceanwanderlust LIVE PLC Questions And Answers 5 December 15th, 2014 01:57 PM
Omron NS10 Ethenert Coms to S7-300 PLC ricoghardforth LIVE PLC Questions And Answers 1 February 19th, 2014 01:27 PM
Omron Communications Cable SouthPahw LIVE PLC Questions And Answers 8 June 14th, 2011 06:54 PM


All times are GMT -5. The time now is 05:22 PM.


.