Old October 19th, 2017, 07:11 PM   #1
DoubleJ
Member
United States

DoubleJ is offline
 
Join Date: Oct 2017
Location: midwest
Posts: 7
1769-L18ER-BB1B issue

I recently started with a new controller. I flashed the firmware which went well and downloaded the program. Everything went good. I shut it off before I left and came in the next day and that is when the problem started. It now says all I/O is not responding even the local in the controller. I tried to reinstall the program and it continues to say that it does not respond. I flashed the firmware and reinstalled again and continues to not see the I/O. All of them have a yellow triangle on them.
  Reply With Quote
Old October 19th, 2017, 07:43 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,007
What is the error code for the connection failure ?

There was a v20 bug with the 1769-L1 controllers where the POINTBus firmware could be incorrectly installed when you flashed over Ethernet, but it worked over USB. Knowledgebase Article 519117, but it was in 2012 so it might not be your issue.

This is almost certainly going to require some input from Rockwell Automation Tech Support.
__________________
- "Simpler is better, except when complicated looks really cool."
  Reply With Quote
Old October 20th, 2017, 04:25 PM   #3
DoubleJ
Member
United States

DoubleJ is offline
 
Join Date: Oct 2017
Location: midwest
Posts: 7
I am using v30 firmware. I did however figure it out today. I flashed the firmware one more time and it completed right away after polling for power up which it had not done in the past. I downloaded the program and everything was good. I disconnected and when I removed my usb cable the network statuses all began to flash red again. I got back online and seen all the I/o was not responding again. Fault was timed out response. I began to think this was a communication issue with the cards because I cycled power and they were fine again. So I decided to remove the first distributed point I/O module next too the plc and replace the base and took care of the problem. It has not reoccurred since. Now onto an interesting issue is I have two outputs that are on with no addressing to them, if I give them an address in the program they turn off and respond as if they should. Odd
  Reply With Quote
Old October 21st, 2017, 11:21 AM   #4
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 390
What do you mean they are on when not addressed? Do you mean you don't call them with an OTE instruction? If so, they will just retain their last state, which may have been ON.
  Reply With Quote
Old October 22nd, 2017, 06:29 PM   #5
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,611
Rupej is onto it - an output doesn't turn off just because nothing is telling it to turn on, it only does explicitly what it's told.

If you have an OTE addressed to that output, the OTE when true will explicitly tell the output to turn on. If the OTE is false, it will explicitly tell the output to turn off. If the OTE is true (and the output is on), and you delete the OTE, there is nothing telling the output anything at all, so it does exactly what it was last told to do until something comes along to tell it differently.

You can monitor it in the controller tags window and write a zero into it's address; that'll turn it off manually.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB DeviceNet Scanner Issue (1769-SDN) pickerel LIVE PLC Questions And Answers 5 April 10th, 2018 09:37 AM
Siemens ET200b issue dwoodlock LIVE PLC Questions And Answers 3 January 7th, 2014 01:31 PM
Intermittent & stubborn issue with Sercos network rguimond LIVE PLC Questions And Answers 8 November 28th, 2013 03:32 PM
Red Lion G307 Kadet Ghosting Issue psychosunshine LIVE PLC Questions And Answers 13 March 20th, 2013 01:26 PM
Safey issue with motors & VFDs kolyur LIVE PLC Questions And Answers 31 September 1st, 2005 07:07 PM


All times are GMT -5. The time now is 04:18 AM.


.