Hi everyone! It´s just a begginer question, isn´t a real case:

In a ethernet ring topology, I read that especific protocols take care about the redundancy (RSTP, STP, etc).

Question: If I have 4 swtches in this ring, all of then need to be managed? It´s possible to use just 1 managed and 3 unmanaged? All elements need to be RSTP able?

Thanks in advance!
 
I do not know of any unmanaged switch that supports any kind of ring protocol so, yes, you need all the switches IN THE RING to be managed.

Also, it worth to note that very RSTP and STP isn't fast enough for industrial application, therefore, each vendor comes up with their own version of ring protocol so you also need to match the exact brand and product-line.
 
I would not bother with a ring within a plant, they are not worth the trouble. Use star or redundant star.

Only between buildings, plants, cities etc would I consider a ring topology
 
I do not know of any unmanaged switch that supports any kind of ring protocol so, yes, you need all the switches IN THE RING to be managed.

Also, it worth to note that very RSTP and STP isn't fast enough for industrial application, therefore, each vendor comes up with their own version of ring protocol so you also need to match the exact brand and product-line.

Agree that STP/RSTP aren't typically fast enough for industrial applications, and that managed switches are definitely required. However, there are some protocols I've seen that are at least somewhat multivendor.

MRP is built into a lot of Profinet devices, and is supported by switches from at least Cisco and Hirschmann, in addition to Siemens. Claims to have a max 200ms failover for 50 devices in the ring (note that's a max, many other protocols advertise a minimum)

HSR is a bumpless ring architecture, where the packets are sent both directions. Again, I've seen support from Cisco, Hirschmann, and Siemens. Downside here is that few devices will support this, probably only switches.

DLR is tied to EIP, and I've seen support from Cisco, Hirschmann, and Rockwell.
 
I would not bother with a ring within a plant, they are not worth the trouble. Use star or redundant star.

Only between buildings, plants, cities etc would I consider a ring topology


Actually, I routinely use rings inside plants. Lots of benefits, particularly with on-machine devices. Or maybe I should just say star is fine, but NEVER use linear in a production facility.
 

Similar Topics

Hi everyone, I don't know much of PLCs but it happened that i need to connect Leuze AMS358i Ethernet laser measurement to Productivity 1000...
Replies
0
Views
1,061
When configuring redundant ethernet cards, will the mac address change along with the IP address. A friend is having problems with IP security...
Replies
3
Views
1,261
Hello all... Have a Powerflex 753 with an Ethernet card communication with a L19ER processor. Here is my setup... Local AB PLC will control the...
Replies
6
Views
1,679
Recently we've had some faults and disconnects with our 1734 aent/r module. It shuts down all processes associated with the remote IO, obviously...
Replies
8
Views
3,345
Hello Team, Is there a way to explore DH+ Networks like there is for EIP and Dnet? Thanks! -PreLC
Replies
3
Views
1,713
Back
Top Bottom