Hello,
I used TIA Portal v15.0 to create a project with s7 1511 and wincc rt professional and an IO Controller. using profinet to connect all 3:
The HMI_connection in Tia portal for wincc rt pro -> S7 1500 is set to CP TCPIP. The wincc SQL in services.exe in running. The Computer name isn't changed. The connection between S7-1511 and the IO Controller is OKAY. When i ping my PLC using CMD "ping 192.168.1.91" I get 4 responses. Yet when i run the Wincc RT Pro, it doesn't detect a server so it creates a localhost and when i open WINCCexplorer my project only contain COMPUTER AND TAG MANAGEMENT, no GRAPHICs DESIGNER...... Can someone please help me out. I will add pictures in a pdf file to help with the idea. Thank you for your time and help. |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
I dont have experience with WinCC Pro.
Bit I can guess a few things. 1. On the WinCC Pro PC, you have to set the access point CP-TCP, not S7ONLINE. There is a switch "set automatically" so maybe it is not important. 2. The error message says you have connected the cable to the wrong port. You have configured topology, so the real cabling and port usage must match the configured topology perfectly.
__________________
Jesper ![]() NOTICE: JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm ! Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ |
![]() |
![]() |
#3 | |
Member
![]() ![]() Join Date: Nov 2019
Location: Casablanca
Posts: 17
|
Quote:
Thank you for your reply. For your ideas: 1. In the pg/pc interface i couldn't find cp tcpip 2. And for the connection to the port i tried changing the port but then i lost connection to the wago io controller too which let me assume that the port is correct, and with that port i can load and connect to the plc using tia with no problem. ![]() |
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Nov 2019
Location: Casablanca
Posts: 17
|
It turned out to be windows firewall. Figures
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Connection between S7 and PC-Windows: PRODAVE, WinCC, OPC Server or ProTool? | urk | LIVE PLC Questions And Answers | 29 | October 24th, 2017 03:40 AM |
WinCC V13 profibus connection to Proxy | JDCROCKETT724 | LIVE PLC Questions And Answers | 7 | May 9th, 2014 02:40 PM |
communication wincc .Q series and s7 300 | ajay34 | LIVE PLC Questions And Answers | 0 | March 30th, 2013 04:54 AM |
"Change connection" in WinCC Flexible and Finding the Master Connection | lkwythe | LIVE PLC Questions And Answers | 7 | March 11th, 2013 04:26 PM |
WinCC keyboard and remote connection | aikona | LIVE PLC Questions And Answers | 3 | April 22nd, 2009 05:06 AM |