Control Logix relay output trouble

This is my second Control Logix project unfortunately it’s giving me fits. The worst part is it’s with something as simple as a relay output card. My trouble is the outputs are on when there is nothing telling them to be on (all 16 outputs). Even if I force them off they are on. The indicator lights on the output card are off but the voltmeter reads 115.6 volts AC for OFF and 117.5 VAC ON or FORCED ON.
I’ve replaced the Output card and the harness connector but get the same result. Funny thing is the relay output card right next to it works just fine.
???
  Reply With Quote
Old September 16th, 2003, 12:37 AM   #2
rsdoran
Lifetime Supporting Member
United States

rsdoran is offline
 
rsdoran's Avatar
 
Join Date: Apr 2002
Location: Birmingham, AL
Posts: 7,371
Are the devices attached to it actually on?

Is the meter reading some form of leakage..can get funny with plc cards.

Have you checked the backplane connector etc etc to make sure card isnt getting "shorted" to power? Are there any substances that could get to rack or ? and create a short?

Have you attempted to use another card in that slot to see if it will work?

These are all general ideas to help determine the problem, I am not familiar with ControlLogix but other AB systems show these kind of problems from time to time,
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."
  Reply With Quote
Old September 16th, 2003, 12:41 AM   #3
Pierre
Lifetime Supporting Member
Vatican City State

Pierre is offline
 
Pierre's Avatar
 
Join Date: Apr 2002
Location: Montreal
Posts: 1,669
Sometimes just using an old meter with a needle will tell you a lot. Try it.

Those nice LCD electronic meters are not always giving us the real McCoy.

See? When in doubt, accuse the techy
__________________
If it looks like a Cat...
  Reply With Quote
Old September 16th, 2003, 12:50 AM   #4
Alan Case
Lifetime Supporting Member
Australia

Alan Case is offline
 
Alan Case's Avatar
 
Join Date: Apr 2002
Location: Wagga Wagga
Posts: 1,268
Put a bit of load on one of the outputs, I suggest a household light globe and then check the voltage. You will find it will be 0. (I hope)
  Reply With Quote
Old September 16th, 2003, 01:20 AM   #5
gbradley
Lifetime Supporting Member
United States

gbradley is offline
 
gbradley's Avatar
 
Join Date: Apr 2002
Location: Corona, Ca.
Posts: 1,637
Misery Loves Company!

LED.... Don't feel bad!
Once I changed out an entire SLC150 before I caught on.
  Reply With Quote
Old September 16th, 2003, 01:24 AM   #6
LED
Member
United States

LED is offline
 
Join Date: Sep 2003
Posts: 2
Yep you guys were right, it’s leaking voltage. I used a panel light with a transformer and it pulls the output down to about 2 volts. The leaking voltage is enough to create trouble with my DC motor controllers so I’ll have to resort to pull down resistors.
You would think with relay output cards it would be like an open circuit with no voltage leaks. Oh well.
Thanks for the help!
  Reply With Quote
Old September 16th, 2003, 10:02 AM   #7
93lt1
Member
United States

93lt1 is offline
 
93lt1's Avatar
 
Join Date: Apr 2002
Location: Mount Pleasant, Iowa
Posts: 994
Are you sure it's a relay card?

Whant is the part number?
  Reply With Quote
Old September 16th, 2003, 10:23 AM   #8
Pierre
Lifetime Supporting Member
Vatican City State

Pierre is offline
 
Pierre's Avatar
 
Join Date: Apr 2002
Location: Montreal
Posts: 1,669
Quote:
Originally posted by LED
You would think with relay output cards it would be like an open circuit with no voltage leaks.
EXACTLY!

Relays will not leak.

Investigate firther.
__________________
If it looks like a Cat...
  Reply With Quote
Old September 16th, 2003, 11:09 AM   #9
LEN
Member
United States

LEN is offline
 
Join Date: May 2003
Location: Michigan
Posts: 12
Control Logix relay output trouble

I know AB PLC 2 and 5 contact outputs have surge protection across the contacts of the outputs. I assume the Logix relay outputs have this also and the leakage is a result of the RC suppression wired in parallel.
  Reply With Quote
Old September 16th, 2003, 11:30 AM   #10
93lt1
Member
United States

93lt1 is offline
 
93lt1's Avatar
 
Join Date: Apr 2002
Location: Mount Pleasant, Iowa
Posts: 994
I did some diggin...

I found the manual for an "isolated contact output module" and though I didn't see anything about surge protection, I did see a "maximum off-state leakage current" in the specifications, so there must be some kind of protection.
Attached Images
File Type: gif contact output.gif (22.0 KB, 160 views)
  Reply With Quote
Old September 16th, 2003, 12:06 PM   #11
hesham
Member
Egypt

hesham is offline
 
hesham's Avatar
 
Join Date: Jan 2003
Location: cairo
Posts: 328
ground connection

Led
I think that all what are you measuring is strays .Please check your ground connection if it's not connected all the pointa will be floating points and will give you what you read in your meter.
i hope it will be so.
good luck
__________________
Hesham Farid
Egypt
------------------------------------------------------------------------
Let your plans be dark and impenetrable as night, and when you move, fall like a thunderbolt(Sun Tzu) .
  Reply With Quote
Old September 16th, 2003, 12:19 PM   #12
Danyan
Member
United States

Danyan is offline
 
Join Date: Sep 2003
Location: Illinios
Posts: 1
Wink relay outputs

This got me the first time also. If you check the card my guess is that it uses triacts for the relay. These cards will display a false voltage when no load is applied. If the output light is off than more than likely you actually have no usable voltage. Try hooking up a device such as a relay or solenoid. You should be able to easily see if everything is working right by forcing the output on and off. My guess is that the card that you replaced is good. I hope this fixes your problem.
  Reply With Quote
Old September 16th, 2003, 01:23 PM   #13
93lt1
Member
United States

93lt1 is offline
 
93lt1's Avatar
 
Join Date: Apr 2002
Location: Mount Pleasant, Iowa
Posts: 994
Re: relay outputs

Quote:
Originally posted by hesham
Please check your ground connection if it's not connected all the pointa will be floating points and will give you what you read in your meter.
Remember that this would only (kind of) apply if the "meter" was using ground as the reference. If he is checking from the "com" terminal on the card to each individual output, then there wouldn't be any "floating points"

Last edited by 93lt1; September 16th, 2003 at 01:28 PM.
  Reply With Quote
Old September 16th, 2003, 03:59 PM   #14
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,311
The 1756-OW16I doesn't use totally dry contacts like the 1756-OX8I does. There is a built-in RC network for surge suppression, and that's what is leaking the 1.5 milliamperes or so, and causing your confusing meter readings, and misleading your DC motor controllers.

You can see it in the user manual (though it's not in the Installation Instructions):

[attachment]
Attached Images
File Type: gif ow16i_schematic.gif (2.4 KB, 111 views)
__________________
- "Simpler is better, except when complicated looks really cool."
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
How can I protect of output of relay (PLCs or some relay) Valera LIVE PLC Questions And Answers 7 December 2nd, 2004 03:43 AM
Memory Allocation in Control Logix Ashwin LIVE PLC Questions And Answers 7 March 5th, 2004 01:44 AM
Looking for Solid State Relay control..... paradym LIVE PLC Questions And Answers 16 June 19th, 2003 08:10 AM
Sequential Logic to AB PLC Tze LIVE PLC Questions And Answers 7 January 4th, 2003 01:41 PM
Panel View & Control Logix gizmo LIVE PLC Questions And Answers 8 September 21st, 2002 11:52 PM


All times are GMT -4. The time now is 07:52 AM.


.