RSLogix 5000 and Powerflex 525.
Hi all,
I'm trying to control several PowerFlex 525 with a CompactLogix 1769-L33ER via Ethernet. I used the EDS Wizard to install the corresponding EDS files and the registration seems to be successful (the PowerFlex 525 devices appear available to unregister, for example). However, when I try to add a PF 525 by right clicking at I/O Configuration -> Ethernet and selecting "New Module", the PowerFlex 525 devices are not available in the device list. The PowerFlex 40, 70 and 700 are available, though. What I am missing? Thank you in advance! |
![]() |
![]() |
#2 |
Member
|
Just going from Memory but i think you need the Powerflex 525 AOP
|
![]() |
![]() |
#3 |
Member
|
If you have an older version of 5000, it may predate the addition of the 520 series, so yes, you will need to add the AOP (Add On Profile), or maybe it's time to update your 5000. There may be other issues.
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Oct 2004
Posts: 588
|
You need the Add on Profile which you can download from the Rockwell site but be very careful. The current version of the AOP installation software uses the "new" database method for handling EDS files so once you have used it any software you have which relies on the old registry system will no longer work. This mainly affects RSNetworx packages but there are some others. Unlike L5K V21 and above which inform you about this the AOP installer just does it and leaves you an unpleasant surprise.
__________________
“What are the facts? Again and again and again-what are the facts? Shun wishful thinking, ignore divine revelation, forget what “the stars foretell,” avoid opinion, care not what the neighbors think, never mind the unguessable “verdict of history”–what are the facts, and to how many decimal places? You pilot always into an unknown future; facts are your single clue. Get the facts!” Robert Heinlein.
|
![]() |
![]() |
#5 |
Lifetime Supporting Member
![]() ![]() Join Date: Apr 2008
Location: NC
Posts: 926
|
I added the (correct) AOP and it worked!
I had added the incorrect AOP by mistake. Thank you! |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Powerflex 753 with I/O Module & RSLogix 5000 | Matt1234 | LIVE PLC Questions And Answers | 10 | March 23rd, 2016 09:35 AM |
Powerflex 525 Multidrive issues | Teglaco | LIVE PLC Questions And Answers | 2 | July 14th, 2014 01:57 PM |
Powerflex 40 on Rslogix 5000 | MattEveritt6 | LIVE PLC Questions And Answers | 5 | March 28th, 2014 06:10 AM |
help with Rslogix 5000 and powerflex 40 | stu | LIVE PLC Questions And Answers | 1 | March 5th, 2013 09:55 AM |
RSLogix 5000 Fatal error when adding a Powerflex 70 Enet | steveb1475 | LIVE PLC Questions And Answers | 2 | January 27th, 2011 07:15 PM |