Old June 13th, 2017, 11:48 AM   #1
Sparkyman1
Member
United States

Sparkyman1 is offline
 
Join Date: Apr 2017
Location: Minnesota
Posts: 32
Duplicate Destructive bits used EVERYWHERE!

What do you guys think of the use of duplicate destructive bits for the ONS tags? This exact same setup is used in many other places in the program, it hasn't ever caused a problem, just curious about everyone's opinion.

  Reply With Quote
Old June 13th, 2017, 11:57 AM   #2
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 356
That logic design makes my head hurt...

But I guess if it's totally segregated like that, there shouldn't be a problem. I know relatively less than most on this forum though
  Reply With Quote
Old June 13th, 2017, 12:06 PM   #3
harryting
Lifetime Supporting Member
United States

harryting is offline
 
harryting's Avatar
 
Join Date: May 2002
Location: Puget Sound
Posts: 1,586
I'm just surprised that it works. A bigger issue is why a binary-state function is represented by TWO bits and just one.
  Reply With Quote
Old June 13th, 2017, 12:19 PM   #4
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 356
Oh yeah I was just looking at the one shots with the XIOs... I dunno how that would work with the unlatch bits for the BTTN before the other logic. That seems overly complex for the job it's doing
  Reply With Quote
Old June 13th, 2017, 12:20 PM   #5
keshik
Lifetime Supporting Member
Canada

keshik is offline
 
Join Date: Jun 2011
Location: Portland, OR
Posts: 327
I think that the duplicate ONS bit is required to make it function. It looks like the "EnablePb" toggles the "Enabled" bit on and off and the "DisablePb" toggles the "Disabled" bit on and off. I think that the ONS storage bit is still on when it gets to the second branch (the OTU one). This prevents the "Disabled" bit from being unlatched immediately.
  Reply With Quote
Old June 13th, 2017, 12:21 PM   #6
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 3,959
Totally absurd piece of code - way overkill !

I'm happy with the pushbuttons (from the HMI) and their respective OTU's, but....

If Roaster05 is disabled - it can't be enabled, and vice-versa, so why have separate bits for enabled and disabled ?

And there's no need for One-Shots at all....

Here's my take on it, tested, working, although I don't see why you need the "Disabled" state bit, you can just use XIO Enabled...

EDIT : You don't need the 3 instruction on the first two rungs either.....
Attached Images
File Type: jpg 2017-06-13_181911.jpg (25.6 KB, 296 views)
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old June 13th, 2017, 12:25 PM   #7
keshik
Lifetime Supporting Member
Canada

keshik is offline
 
Join Date: Jun 2011
Location: Portland, OR
Posts: 327
Quote:
Originally Posted by daba View Post
Totally absurd piece of code - way overkill !

I'm happy with the pushbuttons (from the HMI) and their respective OTU's, but....

If Roaster05 is disabled - it can't be enabled, and vice-versa, so why have separate bits for enabled and disabled ?

And there's no need for One-Shots at all....

Here's my take on it, tested, working, although I don't see why you need the "Disabled" state bit, you can just use XIO Enabled...

EDIT : You don't need the 3 instruction on the first two rungs either.....
I'd be careful about implementing that logic. Just because "Enabled" and "Disabled" have opposite meanings in the English language doesn't mean that they are used that way in the PLC program.

That being said, it does seem like an odd way to have the original program, and probably adds a lot of unnecessary complexity (the fact that the OP is asking questions about it is an indication of that) to the program.
  Reply With Quote
Old June 13th, 2017, 12:27 PM   #8
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 3,959
Quote:
Originally Posted by keshik View Post
I think that the duplicate ONS bit is required to make it function. It looks like the "EnablePb" toggles the "Enabled" bit on and off and the "DisablePb" toggles the "Disabled" bit on and off. I think that the ONS storage bit is still on when it gets to the second branch (the OTU one). This prevents the "Disabled" bit from being unlatched immediately.
I certainly would not want my HMI Enable PB toggling the Enable State on and off - to my way of thinking Roaster05 can either be Enabled, or Disabled, mutually exclusive, and not neither !!
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old June 13th, 2017, 12:29 PM   #9
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 3,959
Quote:
Originally Posted by keshik View Post
I'd be careful about implementing that logic. Just because "Enabled" and "Disabled" have opposite meanings in the English language doesn't mean that they are used that way in the PLC program.

That being said, it does seem like an odd way to have the original program, and probably adds a lot of unnecessary complexity (the fact that the OP is asking questions about it is an indication of that) to the program.
You could be right there, I didn't look hard enough... I'll code it and see what happens .... watch this space ...
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old June 13th, 2017, 12:41 PM   #10
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 3,959
Well here's the original code, and yes keshik is correct, the "Enable" Pushbutton definitely toggles the "Enabled" state on and off....

And the "Disabled" pushbutton toggles the "Disabled" state on and off.....

But look what happens when you "Enable" (when it isn't enabled), then "Disable" (when it isn't disabled) ....

Very curious indeed, and as keshik points out it might be a lack of documentation... and I've just noticed the "Enable" and "Disable" pushbuttons are documented as having come from different "old screens" - perhaps the screens were synchronised to the state of the Roaster being enabled, or disabled, then it might make some sense....

I'd be worried if those "old screens" had been combined into one, then the interlocks would need to be on the pushbuttons themselves...

Not going to knock myself out on this - if it works, fine, if it doesn't, or could potentially fail, I would change the logic.....
Attached Images
File Type: jpg 2017-06-13_183339.jpg (25.4 KB, 287 views)
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old June 13th, 2017, 12:43 PM   #11
mobsoft
Member
United States

mobsoft is offline
 
Join Date: Jun 2013
Location: Bowling Green, KY USA
Posts: 13
I would change the second use of the ONS for each rung into an XIO.

Then it would be a fairly common flip-flop circuit.
  Reply With Quote
Old June 13th, 2017, 12:53 PM   #12
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 3,959
Quote:
Originally Posted by mobsoft View Post
I would change the second use of the ONS for each rung into an XIO.

Then it would be a fairly common flip-flop circuit.
That's only if that was the intention....
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old June 13th, 2017, 02:05 PM   #13
mobsoft
Member
United States

mobsoft is offline
 
Join Date: Jun 2013
Location: Bowling Green, KY USA
Posts: 13
Quote:
Originally Posted by daba View Post
That's only if that was the intention....
Agree
  Reply With Quote
Old June 13th, 2017, 02:25 PM   #14
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,255
Quote:
Originally Posted by daba View Post
That's only if that was the intention....
More likely: the Roaster has two separate states Enabled and Disabled; they are (theoretically!)'related' to each other but not logically interlocked (there is no reference to the other state in each's command logic) hence the need of a 'Push-ON/Push-OFF' same operator sequence for each state's control.

Or at least that's what I am reading...
  Reply With Quote
Old June 13th, 2017, 02:31 PM   #15
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 2,960
The hair on the back of my neck goes straight up when I see lots of one shots and latches used and bad memories come to the forefront. Early in my career I tried to fix some of these, now I won't touch it. I don't want to own it.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
InOut Tags and Duplicate Destructive Bit warnings ASF LIVE PLC Questions And Answers 0 August 18th, 2015 01:10 AM
Sequencers randy LIVE PLC Questions And Answers 43 December 20th, 2014 03:10 PM
can you specify bits in omron PLC's maintenance@seta LIVE PLC Questions And Answers 5 January 6th, 2011 03:54 AM
Bits and more bits, chess, bit boards and tidbits. Peter Nachtwey LIVE PLC Questions And Answers 3 May 3rd, 2007 03:21 PM
Please Explain blackslipper LIVE PLC Questions And Answers 7 December 27th, 2005 01:14 AM


All times are GMT -5. The time now is 03:22 AM.


.