Old June 16th, 2017, 08:52 AM   #16
AutoMax
Lifetime Supporting Member
United States

AutoMax is offline
 
AutoMax's Avatar
 
Join Date: Apr 2017
Location: Indiana
Posts: 217
Well, I'll illustrate something you may be unaware of in the UK as I believe even your homes single phase power outlets have two powered legs. In America, our standard power outlets have one energized leg and a "neutral" that is grounded at the service entrance and the utility transformer. It is also not uncommon to find this power structure in our control cabinets. Not only are the loads on these circuits a very common source of noise, if the primary ground to a panel like this becomes compromised everything formerly grounded becomes energized. This is certainly a dangerous situation, but American maintenance electricians (well qualified individuals, anyway) are aware of this. In such a situation the DC- would also begin carrying hazardous loads.
I'm just providing the scenario because you asked...
  Reply With Quote
Old June 16th, 2017, 09:02 AM   #17
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,255
Quote:
Originally Posted by AutoMax View Post
I believe even your homes single phase power outlets have two powered legs.
I dunno about that...European 230 VAC Single-Phase is identical to the US one in each and every respect except the voltage level and cycle frequency; 230 VAC vs. 120 VAC and 50Hz vs. 60 Hz.

There are three 'legs'; one 'hot', one 'neutral' and one 'safety ground'; different colors (BR, BLU, YEL/GRN) however, electrically (except 'hot' voltage amplitude and frequency) identical.

Last edited by dmargineau; June 16th, 2017 at 09:05 AM. Reason: Added Hz differences.
  Reply With Quote
Old June 16th, 2017, 09:37 AM   #18
AutoMax
Lifetime Supporting Member
United States

AutoMax is offline
 
AutoMax's Avatar
 
Join Date: Apr 2017
Location: Indiana
Posts: 217
Interesting... I've never worked on European residential systems, but when working in Europe with systems with 120v power destined for the US they did not ground one leg of the transformer, yielding a 60v/60v system rather than 120v/0v. I made the assumption (perhaps foolishly) that they wired their houses like that.
Also, I've serviced British two-phase machinery (nightmare.) Perhaps that contributed to my dumb assumptions.
  Reply With Quote
Old June 16th, 2017, 09:39 AM   #19
AutoMax
Lifetime Supporting Member
United States

AutoMax is offline
 
AutoMax's Avatar
 
Join Date: Apr 2017
Location: Indiana
Posts: 217
Also, fwiw, the Japanese seem to always ground their DC-, not their 120v AC, and they use NPN input cards...
  Reply With Quote
Old June 16th, 2017, 09:47 AM   #20
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,255
Quote:
Originally Posted by AutoMax View Post
Interesting... I've never worked on European residential systems, but when working in Europe with systems with 120v power destined for the US they did not ground one leg of the transformer, yielding a 60v/60v system rather than 120v/0v.
That's also very interesting to say the least...

There might've been some end user specifications especially if said 120 VAC was being used in control circuits; I have encountered some nightmare Indramat/Rexroth 24 VAC control circuitry derived from similar 2-Phase 120 VAC (obviously ungrounded) transformers...Not pretty and very dangerous when expanded with US produced 120 VAC devices...
  Reply With Quote
Old June 16th, 2017, 09:52 AM   #21
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,255
Quote:
Originally Posted by AutoMax View Post
Also, fwiw, the Japanese seem to always ground their DC-, not their 120v AC, and they use NPN input cards...
That's a mishap waiting to happen...Any grounded signal wire will turn its associated Input ON...
  Reply With Quote
Old June 16th, 2017, 09:54 AM   #22
AutoMax
Lifetime Supporting Member
United States

AutoMax is offline
 
AutoMax's Avatar
 
Join Date: Apr 2017
Location: Indiana
Posts: 217
Just to be clear, when I said "British two phase equipment", I meant equipment with legs 90 degrees out of phase instead of 180. That is a unique experience.
  Reply With Quote
Old June 16th, 2017, 11:27 AM   #23
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 578
just one thing to think about with the new switched power supplies one leg of the output may be connected to one of the supply legs, every manufacture has there own design and you really should check with them before grounding them or even paralleling the outputs
you could end up causing a more problems.
I have seen a lot of problems with misconnected power supplies.
  Reply With Quote
Old June 16th, 2017, 11:53 AM   #24
JerryH
Member
United States

JerryH is offline
 
JerryH's Avatar
 
Join Date: Mar 2009
Location: Tellico Plains,TN
Posts: 107
Quote:
Originally Posted by AutoMax View Post
Also, fwiw, the Japanese seem to always ground their DC-, not their 120v AC, and they use NPN input cards...
No, the Japanese ground their DC+, and they use PNP input cards with NPN input devices.

Been this way for the two Japanese plants I've worked in.

Jerry
  Reply With Quote
Old June 16th, 2017, 12:03 PM   #25
JerryH
Member
United States

JerryH is offline
 
JerryH's Avatar
 
Join Date: Mar 2009
Location: Tellico Plains,TN
Posts: 107
Quote:
Originally Posted by AutoMax View Post
Also, fwiw, the Japanese seem to always ground their DC-, not their 120v AC, and they use NPN input cards...
Quote:
Originally Posted by dmargineau View Post
That's a mishap waiting to happen...Any grounded signal wire will turn its associated Input ON...
I know this is getting a little off topic but, when the DC- is grounded than you want NPN input cards. A grounded signal wire will not turn in input on. An NPN input card requires a voltage input to turn it on.

Jerry
  Reply With Quote
Old June 16th, 2017, 12:32 PM   #26
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,138
Staying with the off topic, don't get too tied in to the grounding causing a false signal. I was reading some machine fault reports and a surprisingly large number were caused when an unexpected +24V was received by the a system. You think of wires touching earths but theses were mostly crushed multicore cables that then put supplies where there shouldn't be one.

Back on topic-ish. I am not trying to make anyone look foolish, or to put them down. As has been pointed out to me elsewhere recently I sometimes get a bit too impassioned when discussing subjects. If it happened here I apologise.

Back on topic. It is my understanding that in a normal mixed voltage panel it is safer to earth one side of the control supply. If someone can argue that point then I am happy to be corrected. If you accept that it is safer then all other discussions start with 'I choose the less safe option because:' For AutoMax it is 'I choose the less safe option because I was having problems with electrical noise'. I accept that electrical noise can be a problem but the fix makes me nervous. Yesterday I had a customers customer complaining that an over pressure shutdown kept tripping. Their fitter's way to fix the problem was to wire out the sensor. When I logged in they were running a 250bar system at 610bar. They should have fixed the problem and not the symptom.
  Reply With Quote
Old June 16th, 2017, 12:41 PM   #27
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 356
Quote:
Originally Posted by BryanG View Post
When I logged in they were running a 250bar system at 610bar.
  Reply With Quote
Old June 16th, 2017, 01:02 PM   #28
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,255
Quote:
Originally Posted by JerryH View Post
I know this is getting a little off topic but, when the DC- is grounded than you want NPN input cards. A grounded signal wire will not turn in input on. An NPN input card requires a voltage input to turn it on.

Jerry
In my previous post I was referring to NPN field Input type devices connected to their corresponding Input modules (NPN type sensor-Sourcing Input modules); a NPN sensor sends the (-) to the input module when changing states; if a NPN sensor system has its 24COM (-) grounded then a shorted NPN sensor Signal wire will falsely trigger its associated Input point.
  Reply With Quote
Old June 16th, 2017, 01:18 PM   #29
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,249
Quote:
Originally Posted by skyfox View Post
Wondering what are the pros/cons of tying Power +24VDC supply Common to chassis (earth) ground. Is it OK to do so? I have seen some control panels where this is done and others without. I have also seen Dual polarity supplies +/-15VDC commons tied to chassis ground as well. What determines if a power supply common should or shouldn't be tied to a chassis ground?

Thanks
The default position that I take is to ground the negative of the power supply. This method enhances stability for analog signals and makes it easier to troubleshoot DC circuits, since they aren't floating. I'm sure that there are valid reasons to avoid earthing some DC power supplies, but those would be the exception to the rule.
__________________
  Reply With Quote
Old June 17th, 2017, 01:16 AM   #30
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 234
Some 24VDC devices ground the common without it being obvious. I seem to remember many AB PanelViews being this way. So if you do intentionally ground the DC common at the power supply, you just created a ground loop and thus a possible noise problem.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
OT: UPS neutrals OkiePC LIVE PLC Questions And Answers 15 December 17th, 2015 01:16 PM
Advice for connecting ground of RS 485 in PLC arbj LIVE PLC Questions And Answers 6 October 10th, 2015 01:30 PM
Single ended vs Differential learner LIVE PLC Questions And Answers 3 December 15th, 2010 11:34 AM
" do not care for AC connection " is this statement correct ?? magdyfayad LIVE PLC Questions And Answers 26 October 3rd, 2008 09:52 AM
Transformer wierd voltages leitmotif LIVE PLC Questions And Answers 32 September 21st, 2008 02:34 PM


All times are GMT -5. The time now is 09:42 AM.


.